Just as a point mobile homes semi permanent are required to have a PIR or in new parlance an electrical condition report when they are moved and reconnected they are also required to have an annual PIR if they are to be hired.All mobile homes we site are given a PIR after connection. It's amazing how many times RCDs fail testing, on a caravan site there are probably many many more RCDs than domestic guys come across.I wouldnt trust my life to an RCD. Just as an aside to BS7671 I have a system that runs 600v chopped DC at 20KHZ in water it is protected by a 9mA earth leakage detector and a continuous insulation test that trips if below 1.5Mohms. Would you go near it if protected by a commercial 30mA RCD
Fully agree with you there on the total reliance of an RCD device Mike!! Which is why i consider this BS 7671 200 ohm Ra level for a TT system, as a total farce.
We try and get earth spike Ras below 10 ohms either by multiple spiking or other earth plate arrangements. BS 7671 doesn't give a calculated reason for the 200 ohm other than its likely to be unstable above this in my experience and Ra of 200 ohms is practically unacceptable it would certainly lead to a touch voltage over 50V which is what i thought the regs were all about keeping touch voltage below 50V
Reply to Static or not in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...