Hi guys, I may sound like a bit of a thicko but I am puzzled by something at the mo. I am installing a 7.5kW 3P balanced submersible pump in a concrete collection chamber. The sealed leads that came with the pump were not long enough to reach the control box so I was given a resin joint kit to join the existing leads with some armoured - the joint will be submersed in water most of the time. There is no earthing point on the pump, no mention of it in the manual.

So my question is: if there is a fault, either on the metal casing of the pump or the resin joint fails, what happens to the fault current? I am a bit concerned because it is very muddy and wet around the chamber and control box so anyone near by may be affected.

Thanks
Adam
 
Think you will find even though there is metal parts on the pump it is a double insulated pump/motor and that is why there is only 3 cores .

Normally pumps like this come with a lead some 20 metres long if you have not already purchased it you could contact the manufacturer of the pump they may supply you with one with a cable as long as you want
 
Last edited:
can you purchase a longer cable of the same type /size and remove short piece and replace with longer cable then you have no joint to worry about
 
ok thanks guys. any ideas on the earthing problem?

You don't have an earthing problem if it's double insulated (Class11)!! If there is no connection means within the sealed motor cable, and no means of earthing on the motor housing then you can be pretty dammed sure it IS a Class 11 submersible pump!!!
 
silly me. looked today and there is an earthing nut. seems a bit stupid to me that theres nothing in the manual about it. you would think that the pump would have some sort of multicore cable with the 3 phases + an earth. I suppose i'd better put a new earth rod in at the control box because its about 400M away from the dis board!
 
silly me. looked today and there is an earthing nut. seems a bit stupid to me that theres nothing in the manual about it. you would think that the pump would have some sort of multicore cable with the 3 phases + an earth. I suppose i'd better put a new earth rod in at the control box because its about 400M away from the dis board!

Don't be silly!! The chances are this submersible IS Class 11 and has no need for an earth connection. As for the 400 metre run, i hope you've calculated for the volt drop on this motors starting current?? How is this supply cable to the pump being run and in what type of cable??
 

Reply to Submersible Pump... in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This thread can now be closed, as I seem to also have space in the box for the first switch. Revised diagram below. Thanks folks.
Replies
6
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top