IET Forums - Underground SWA Current Rating? - http://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=27920
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Suggestions for best way to wire underground supply please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
That part would be ok - 89A clipped direct or 97A in free air ?What about the part of the cable that comes out of the ground?
Based on 30 degrees tho yes?That part would be ok - 89A clipped direct or 97A in free air ?
Only if you pay my electric billas an experiment, try shoving 100A down some 16mm for an hour. then measure the temp. of the cable. if you read >40deg.C. then your temp gauge is wrong.
Well it errs on the side of safety but I didn't write the regs , send any complaints to jpel/64 hawe not in the sahara . not even spain. 30deg. my arse. we'd all be like essex boys at that temp.
Yes, 4D4A is for ambient air temp of 30. Still thinking ...Based on 30 degrees tho yes?
The overall ccc of the cable needs to be the lowest rating if installed using different reference methods using the most onerous methodYes, 4D4A is for ambient air temp of 30. So for cable in free air Ref E - well the cable isn't buried any more - so 433.1.203 doesn't apply and that part of the cable doesn't need derating from what's listed in the table ?
I would assume tests would have been performed and the appropriate ccc recorded as we see them today.haha, trouble is that the regs. are so pessimistic. written to cover arses. as a famous person once said." rules are for the strict adherence of fools, and for the guidance of wise men"
Don't thank me yet wilko as someone might come along and shoot me down in flames.Got it - thanks Ian
Ha ha, always on the cards !Don't thank me yet wilko as someone might come along and shoot me down in flames.
It's how I understand it and it's written in be 7671 so got to go with that don't we?
Reply to Suggestions for best way to wire underground supply please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net