Ha ha, always on the cards !
I needed to re read 433.1.203 a few times. Using an 80A fuse for overcurrent protection of a buried cable then the cable needs to be rated >=89A and clearly 16mm isn't when it's buried :)
Have a read of guidance note 6.
A lot more clear on the subject.
IET Guidance notes are our friends :)
 
Good thought - I've 1, 3 and 8 now I've a reason for 6 :)
I'm the same except my 3 is to the green version of bs 7671 and only bought it for my testing exam.
Don't see the point in renewing it as all that's changed is the zs values in the book
 
Why would buried in the ground be considered more onerous for current rating than clipped direct/'free air' . Doesn't make sense to me.
 
Why would buried in the ground be considered more onerous for current rating than clipped direct/'free air' . Doesn't make sense to me.
It's ability to dissipate heat is worse when it's buried would be my guess, especially if installed in a pvc duct.
Despite giving an ambient temperature of 20 degrees buried
 
Why would buried in the ground be considered more onerous for current rating than clipped direct/'free air' . Doesn't make sense to me.
I know what you mean! Looking into it a bit (feedback appreciated)
Table 4B3 gives rating factors if we know the soil thermal resistivity on the site. Otherwise we use the tabulated ccc of Table 4D4A column 6 (say) which are worked out for 2.5K.m/W. Looking on internet (no warranty there) for thermal conductivity and using 4B3 for rating factors :
- dry soil 3.3 - rating factor 0.9
- damp sandy soil 0.5 - rating factor 1.88
So local conditions could change the rating quite a lot, and it looks like BS7671 has conservatively punted for dryer soil conditions.
 
I've just done the exact same job, except from a detached garage on an old property. Gas central heating, so used 16mm 3-core swa with a 60amp switch fuse.
 

Reply to the thread, titled "Suggestions for best way to wire underground supply please" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Suggestions for best way to wire underground supply please
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
51

Advert

Thread statistics

Created
The General,
Last reply from
Guitarist,
Replies
51
Views
6,739

Advert

Back
Top