Have a read of guidance note 6.Ha ha, always on the cards !
I needed to re read 433.1.203 a few times. Using an 80A fuse for overcurrent protection of a buried cable then the cable needs to be rated >=89A and clearly 16mm isn't when it's buried
A lot more clear on the subject.
IET Guidance notes are our friends