Supply Isolator required to be metal on TT | on ElectriciansForums

Discuss Supply Isolator required to be metal on TT in the UK Electrical Forum area at ElectriciansForums.net

I assume you are talking about a separate domestic double pole isolator if so, no.
Regulation 421.1.20 of BS 7671:2018 states, for consumer units and similar switchgear assemblies in domestic premises, to be manufactured from non-combustible materials or be enclosed in a cabinet constructed from non-combustible materials.
 
Regulation 421.1.20 of BS 7671:2018 states, for consumer units and similar switchgear assemblies in domestic premises, to be manufactured from non-combustible materials or be enclosed in a cabinet constructed from non-combustible materials.
It does but that doesn't seem to bother the DNO or meter installers, I see lots of plastic DP isolators in plastic enclosures just after the meter.
 
I look at it as a poor way of saying consumer unit or similar i.e. a collection of switches, fuses, circuit breakers or similar protective devices as an assembly.

I do not personally consider a single isolator as falling into the regulation listed above.
 
I look at it as a poor way of saying consumer unit or similar i.e. a collection of switches, fuses, circuit breakers or similar protective devices as an assembly.

I do not personally consider a single isolator as falling into the regulation listed above.
In that case how do yo feel about a "S" RCD upfront in a plastic unit before the main CU.
 
In that case how do yo feel about a "S" RCD upfront in a plastic unit before the main CU.
Rcds are often installed ahead of a consumer unit on a TT supply.
Requiring a metal enclosure would introduce new risks.
 
If incorporated inside a fire retardant meter box, plastic enclosure would be compliant to Regulation 421.1.20 .
Not sure all meter boxes are fire retardant though!
Wording like 'similar switchgear' only helps with various interpretations!

 
If incorporated inside a fire retardant meter box, plastic enclosure would be compliant to Regulation 421.1.20 .
Not sure all meter boxes are fire retardant though!
Wording like 'similar switchgear' only helps with various interpretations!

That is not non combustible
 
That is not non combustible
Indeed. IIRC, when this ridiculous regulation first made the light of day, there were several questions and proposals regarding the use of non combustible plastics, but it turned out that the regulation was framed such that only metal would meet the requirements, without resorting to exotic and expensive materials.
 
I would/have put a plastic enclosure up front with an S RCD in it on a TT install. Tails torqued correctly and ideally checked again the following day, suitably glanded in and out with a tails gland, with the earth hole blanked. I think this is a preferable/less risky scenario than having the metal enclosure with only the main 100A fuse protecting against something shorting to a metal enclosure with rather likely a PEFC of under 10A..
 
How would you feel about a metal enclosure when PSCC/PFC is likely insufficient to take out a main fuse?
Is there not some sort of guidance or similar issued by NAPIT or the NIC that states tails that are securely clamped and glanded in a metal enclosure aren't classed as a risk in a metal TT enclosure.
 

Reply to Supply Isolator required to be metal on TT in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For a TN system neutral is deemed at earth potential.
Replies
6
Views
373
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top