I would be interested to know which of my posts make you think i don't understand the term "extraneous" conductive part, at least i can spell it
By the way in the OSG section 4.7 page 31 it says "supplementary bonding is not required to metallic pipes supplied by plastic pipes"
apologies as well if i have been a bit off with anyone!
I understand your point entirely. There was a similar thread about this a few weeks ago, someone wanting to know if they needed to bond radiators, and short sections of pipe which were supplied by plastic pipe. Whilst I would agree that there is no need to bond individual radiators, I would still expect a metallic heating system to be bonded.I see what you are saying here....but you cant stop at just plastic sections,compression joints are electrically unreliable,are you going to do a continuity test on every single pipe in the building between each electrically suspect joint and perhaps link across compression joints?
A sledgehammer to crack a nut IMHO....just stick to the requirements of BS7671.
In domestic situations,the minimum cable size to an external building attached to a TNC-s system would be 10mm ( the earth size must be equal to the main protective bonding conductor)
The other way of doing this if your cable to an outbuilding is under sized would be to segregate from the building cpc and install and RCD/RCBO to protect it .
In domestic situations,the minimum cable size to an external building attached to a TNC-s system would be 10mm ( the earth size must be equal to the main protective bonding conductor)
The other way of doing this if your cable to an outbuilding is under sized would be to segregate from the building cpc and install and RCD/RCBO to protect it .
Indeed, main bonding in out buildings, if TNCS supply, should be 10mm min.
One of the reasons for using a rod and divorcing the earth, is to do away with the need to run a separate bond from the "shed" back to the MET in the house.
So can anyone clarify, when specifying a distribution circuit from the main consumer unit in a house to an outbuilding with its own circuits.
If the main house supply is TN-C-S do you need 2core SWA using the sheath as earth or 3core SWA?
Confused!
Thanks Wayne,If there are no extraneous conductive parts in the outbuilding, then you will be able to use either as your CPC for the outbuilding.
If there are extraneous conductive parts in the outbuilding, then you will require a 'protective bonding conductor' to be run to the outbuilding and, in this case, the 'third core' or 'armouring' may not be sufficient.
Hope that's clearer
Also if I wanted to split this supply in a 900mm trench to serve two outside locations what is the preferred method of T ing the cable at that depth?
Sorry to throw another problem into the pot.