Is there no circuit protection?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Swa as main earth ?!? in the UK Electrical Forum area at ElectriciansForums.net
Not at the moment… do the solution I have come up with as the customer doesn’t want to run new cable is… 100amp fused switch then run the armoured . Make it off the other end properly and convert all 3 buildings to ttIs there no circuit protection?
Re done my calves and 16mm I believe… based on 100amp pfc of 658aWhat size main protective bonding is required?
For main protective bond sizes on a TN-C-S system it is based on the DNO supply neutral not PFC.
The supply is 25mmFor main protective bond sizes on a TN-C-S system it is based on the DNO supply neutral not PFC.
This is what Ive got supply end straight into the swa. Earth is 16mmWhat is 25.0, the tails from the head?
What size earthing conductor is installed from the head?
This was why I was thinking TTIf it becomes TT the distribution cpc is not relevant.
This is what Ive got supply end straight into the swa. Earth is 16mm
View attachment 118019
Obviously it's electrically irrelevant and I'm not trying to pick an argument that flies in the face of common sense....If it becomes TT the distribution cpc is not relevant.