im a numpty, if course you cant induct into a non ferrous metal. hence te AWA. I wasnt aware that you can get SWA singles for the reason you mentioned.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss SWA from transformer to DB in the Electrician Talk | All Countries area at ElectriciansForums.net
im a numpty, if course you cant induct into a non ferrous metal. hence te AWA. I wasnt aware that you can get SWA singles for the reason you mentioned.
Neither was I, all the transformers I’ve worked on had either double insulated or lead sheathed tails. Aluminium never crossed my mind!
The thread started with SWA armoured singles!
Sorry this is a bit late.
Armoured transformer tails are unusual, normally double insulated un-armoured. The reason for glanding just one end is to stop the armour wires becoming a giant 1/1 CT. At full load your 500KVA transformer would have 666A flowing in the armours.
I once had a situation where 1000KVA transformer was installed and the contractor decided that the brass gland nuts we’d provided were to nice to use so substituted steel, it was in a bolted terminal box so who would know. Things were OK for a while but as the load on the transformer grew so did the heat. I’m just glad I wasn’t around when the insulation finally melted in the transformer terminal box
The contracting company wasn’t around for long after that!