J

james beckford

I have been asked to install a db in a wooden outbuilding, the building has been erected on the base of an old garage.

There is an old 2 core SWA cable running from the main DB in the house underground coming up in the building

I have tested out all the cables and continuity and insulation all fine, the house is tncs.

My question is this, can i use the armour as the earth back to the main DB ? i fitted the board on and connected in a socket and Zs and trip times all good, well within limits or do i need to replace the old cable with a 3 core ?

ps i have disconnected everything pending solving this problem.

client wasnt too happy when i said that i would prefer to dig out cable, said another sparks had told him it would be fine,

Thanks in advance for the usual helpful answers
 
Someone will be able to tell you, but you will need to provide more information. Cable size, length, load or what the new db is going to supply. Then adiabatic equation, but don't ask me!
 
cable size 4mm2

lenght 10M

2 double sockets and 1 flourescent light

checked all my calcs for votage drop etc etc and was well in.

I was concerned as sub main comes out of non rcd board so was planning on putting powerbreaker adjacent to board

any comments ?
 
Mick,

sorry brain bit slow tonight, are you saying that it is okay to use armour as the earth ?

James
if i gave you a length of 3 core SWA for a 3 phase motor.....would you think it was OK?

or lets say you came across an existing install (single phase) with both live conductors running through a steel conduit...what would you think about it?

i expect answers to both please.
 
d skelton,

its out in the van, i shall go and fettch forthwith.

Glenn,

if i was installing from new i would have put 3 core in but cable already in situ from old building that waqs knocked down, wouldnt use conduit for earth as requires someone to connect it right but armour should be continuos.

Mick,

always taught that armour there in case jonny jcb driver puts bucket through it,

I appear to have asked the wrong question tonight, just trying to avoid going half a mile to garage to get 17th out leaving kids in bed
 
d skelton,

its out in the van, i shall go and fettch forthwith.

Glenn,

if i was installing from new i would have put 3 core in but cable already in situ from old building that waqs knocked down, wouldnt use conduit for earth as requires someone to connect it right but armour should be continuos.

Mick,

always taught that armour there in case jonny jcb driver puts bucket through it,

I appear to have asked the wrong question tonight, just trying to avoid going half a mile to garage to get 17th out leaving kids in bed
is this a true statement James?...
 

Reply to swa submain query in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top