J

james beckford

I have been asked to install a db in a wooden outbuilding, the building has been erected on the base of an old garage.

There is an old 2 core SWA cable running from the main DB in the house underground coming up in the building

I have tested out all the cables and continuity and insulation all fine, the house is tncs.

My question is this, can i use the armour as the earth back to the main DB ? i fitted the board on and connected in a socket and Zs and trip times all good, well within limits or do i need to replace the old cable with a 3 core ?

ps i have disconnected everything pending solving this problem.

client wasnt too happy when i said that i would prefer to dig out cable, said another sparks had told him it would be fine,

Thanks in advance for the usual helpful answers
 
dave,

think wve gone awry, 3 core wont stop idiots being idiots and wasnt suggesting 3 core would prevent someone putting socket on light circuit, using it as an example to show that people will mess around where they shouldnt,

But you used this as your justification for using 3 core in post #39

"i always use 3 core if im installing, purely cos i dont trust people not to fiddle with nuts and bolts"

Implying that the use of 3 core would be more idiot proof than 2 core.


 
But you used this as your justification for using 3 core in post #39

"i always use 3 core if im installing, purely cos i dont trust people not to fiddle with nuts and bolts"

Implying that the use of 3 core would be more idiot proof than 2 core.


and the saying goes that if it was good for service....when put into service then you cannot be reasonably held accountable to the effects of tampering etc...
likewise with ECRs....as long as it was fit for continued service when inspected & tested.....
 

Reply to swa submain query in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top