J

james beckford

I have been asked to install a db in a wooden outbuilding, the building has been erected on the base of an old garage.

There is an old 2 core SWA cable running from the main DB in the house underground coming up in the building

I have tested out all the cables and continuity and insulation all fine, the house is tncs.

My question is this, can i use the armour as the earth back to the main DB ? i fitted the board on and connected in a socket and Zs and trip times all good, well within limits or do i need to replace the old cable with a 3 core ?

ps i have disconnected everything pending solving this problem.

client wasnt too happy when i said that i would prefer to dig out cable, said another sparks had told him it would be fine,

Thanks in advance for the usual helpful answers
 
Glenn,

i know the answer to this somewhere in the back of my head, something to do with delta operation 230 x square root of something, need to dig out old college notes for full correct answer tho
 
James.............if you ever get the chance to wire up a 3 phase motor you'll find an internal earth connection inside the motor terminal box.

This is 'not' where you terminate the SWA armourings :)
Well..........just my tuppenceworth :cowboy:
 
Right so your 3 core will prevent him doing that will it? No of course it won't.

What exactly is the danger in swapping a light fitting for a 13 amp socket? Sure its plain daft as he wont get more than 6 amps from a normal domestic lighting circuit.
Does beg the question of what he was growing in a hydroponics setup in a loft? Surely you'd want your supply of fresh herbs a bit closer to the kitchen?
 
help im sinking, just got calculator out and must be square root of 3, 3 being number of phases, still not totally sure where calculation come from in the first place tho, maths never my stongest area
 
dave,

think wve gone awry, 3 core wont stop idiots being idiots and wasnt suggesting 3 core would prevent someone putting socket on light circuit, using it as an example to show that people will mess around where they shouldnt,

on the lighting one it was an old re wirable and hed upped it, hence the prblem

ps got that one from a fireman mate who had to water the plants as it were when it went up
 
Right so your 3 core will prevent him doing that will it? No of course it won't.

What exactly is the danger in swapping a light fitting for a 13 amp socket? Sure its plain daft as he wont get more than 6 amps from a normal domestic lighting circuit.
Does beg the question of what he was growing in a hydroponics setup in a loft? Surely you'd want your supply of fresh herbs a bit closer to the kitchen?
the only herbs i have witnessed that required 13A plugtops for lighting were kept well away from kitchens, and any other places where the outside doors were...
 
help im sinking, just got calculator out and must be square root of 3, 3 being number of phases, still not totally sure where calculation come from in the first place tho, maths never my stongest area
maths not mine either...
but its 230 X square route of three...
or 400/ square route of three...
for delta its voltages in series....so you add them up...
the currents divide...
 

Reply to swa submain query in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top