Evening all..

I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the plan was to move the CU under the stairs and get DNO to move the supply to the same place. They have said they cannot move the cutout to where the CU will be. The approx length from cutout to CU will now be around 8m so I need to add a fused switch. My questions are about which type of cable to use:

1. I could use 2 core 25mm SWA (seperate 16mm earth) but I am unsure of how easy this is to bend through the route? It will be going straight up from the meter box and then 90degress into the house wall entering directly under the first floor floorboards. What is the best way to get it through the wall without putting too much strain on it (with regards bending angle)?

2. BS7671 states 25mm to be used, however I am fusing down to 80A, could I not use 16mm SWA as CCC is 87A?

3. Could I use tails as at no point will the tails be buried in the wall. They will be going directly under the floor boards from outside the house (suitable protected outside) and then down from the ceiling directly behind the new CU (there will be a cavity behind new CU as I will bring out from the wall). Do they need to be protected if they are not getting buried in the wall?

4. Which is easier to move around/use T&E (16mm or 25mm), SWA (16mm or 25mm) or tails?

5. Which is the best fused switch to use? KMF, wylex metal? Can I gland SWA into a KMF or does it need an adaptable box?

Cheers chaps:biggrin:
 
Everything can given sufficient heat!
I'm not a scientist, but I think that when metal is heated to a sufficient temperature it changes from a solid state to a molten state. If it's heated to a higher temperature it may actually boil and turn into a gas. To catch fire, is a state of combustion. If metal can be combustible, then it's not gonna be much use as a material for 421.1.201. :)
 
I've used a few of these to supply submains etc & I agree top value and a decent quality unit,but I've been thinking...what about amendment 3? they don't comply eh?

I would say that they do comply when installed in an external meter cabinet as long as there's a fireproof wall between the cabinet and the inside of the property.
 

Reply to SWA, T&E or tails?? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
663
totally agree
Replies
12
Views
959

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
SWA, T&E or tails??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
75
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top