ok mate no interest elsewhere so here goes........one for your fault archives.
The new 3 phase/N feed into my office block was taken from a joint in the street outside which also feeds street lighting/pump house down the road etc etc.
Turns out the cable/joint/termination ( downstream from us) developed an earth fault on L3/blue phase/grey phase whatever you want to call it
.
This earth fault blew the main fuse in their substation but the heat from the blast ( at the location of the fault) 'welded' L2 and L3 together at the same time clearing the earth fault..........if you get my drift ! lol
This meant L1 was still ok and fused.
L2 was still ok and fused.
L3 was now fused to L2 and being fed through L2 back to my main D/B giving me good tests on all single phases.
Moral of the story........if their is one lol
You can have good tests but still be in a fault situation.
Subsidence seemingly causes this problem on underground cables sometimes but not sure how often..........new one on me that's for sure.
Clear as mud mate