just wondering how you guys,install temp electrics to portacabins
Seen a lot of installs on sites & at schools where I don’t think it’s correct.
Mainly earthing,& earthing conductors,or am I being over cautious,cheers.
 
I'm under the impression that temp supplies have to be TT earthing.
DNO's usually insist on TT earthing for temp supplies. They will not provide PME for temp supplies.
Even if Perm supply, aren't porta cabins classed as temp building as they are movable?
 
I'm under the impression that temp supplies have to be TT earthing.
DNO's usually insist on TT earthing for temp supplies. They will not provide PME for temp supplies.
Even if Perm supply, aren't porta cabins classed as temp building as they are movable?
Thanks,seen so many not tt,& agree Pme should not be used.
 
TT is not always required. TNS is acceptable. A TNCS supply to a transportable unit can be used where the installation is under the continual supervision of a skilled or instructed person. This may be the case in the units you have observed not on a TT
 
I'm under the impression that temp supplies have to be TT earthing.
DNO's usually insist on TT earthing for temp supplies. They will not provide PME for temp supplies.
Even if Perm supply, aren't porta cabins classed as temp building as they are movable?

Any transportable unit will need an earth electrode installed unless it is under the supervision of 'skilled or instructed person(s)' in which case the PME can be used.

Construction sites also need to comply with Section 704 as well as 717.
 
Any transportable unit will need an earth electrode installed unless it is under the supervision of 'skilled or instructed person(s)' in which case the PME can be used.

Construction sites also need to comply with Section 704 as well as 717.
A transportable unit connected to a TNS earth will not need an earth electrode or to be under supervision.
 

Reply to Temporary building supplies again in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top