At a house today to do a job. Had to pull the fuse and found the attached in the meter cupboard. Customer tells me there is another unit in the garage, both serve a caravan (I didn't verify this as it had nothing to do with my work). Both units have had the SWA made-off with BS951 clamps. One of the units was installed yesterday by the 'local' unregistered electrician. Explained to the customer it was wrong, but she didn't care!
[ElectriciansForums.net] Termination of SWA cable
[ElectriciansForums.net] Termination of SWA cable
 
if the box your connecting into is plastic, is it still best to use the frying pan and brass nut and bolt and bring an earth from the bolt to the earth point in the box yea?? even though the box is plastic and not metal?
 
What are peoples thoughts with earthing the banjo or 'frying pan' as named above? I always earth at both ends even if armour is not being used as the cpc. A bloke who I work with just does it at one end when armour is not used as cpc.
 
Last edited:
If the box is plastic, take the CPC straight to the accessory, unless it doesn't need a CPC, such as a switch. In this case, take it to the box.

as for using a banjo, if the item you are glanding to is unpainted metal, then IMO there is no need for the banjo. It is important though, that the glandplate, trunking, conduit box ect is effectively connected to the MET or CPC by a material that has at least the same adiabatic rating as the largest CPC required for the cables. If the armour is used as a bonding conductor for TNC-S, then you need to ensure that the cable used as a link is upto the job using the appropriate table.
 
If the armour is used as a bonding conductor for TNC-S, then you need to ensure that the cable used as a link is upto the job using the appropriate table.​




The SWA would need to be a pretty big cable to allow you to use the armouring as the bonding conductor on a TNC-S system!! lol!!
 
Having not been apprenticed, I have learnt a lot from reading, and seeing/putting right work I have see, that's what's great about this forum, the unwritten, however if I do something for the first time I always consult the experts, I'm qualified, but its no substitute for experience!
 

Reply to Termination of SWA cable in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Sounds more positive.
Replies
8
Views
561
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top