Hi All
Recently joined the forum to ask for some information.
I recently bought a flat to let. I was advised by the letting agent to get the electrics tested, although not a legal requirement. The test was carried out by their electrical contractor. He failed the test due to the fuse board not having an RCD fitted. The fuse board is the original board fitted in 2003 when the flats where built. There has been no mods or circuits added to the system and everything is working as it should. I paid ÂŁ348.00 for the test and the RCD to be installed. I have since been told that the test should not have failed due to the lack of the RCD. Have I been stitched up.
Any comments gratefully recieved

Peter
 
I th

ought it was the opposite supplementary bonding could be omitted if conditions were met and under 701.411.3.3 circuits had to have protection by RCD/RCBO.
For the purpose of an EICR a code 2 would be appropriate only if neither RCD protection or supplementary bonding were in place, if only the latter is present a code 3 is sufficient .
 
Last edited by a moderator:
My understanding, is that installations which complied at the time of design/construction but do not comply with current editions do not require upgrading.
As such anything that complied at the time of design/construction should only warrant a code C3.
As RCD protection for sockets which would reasonably be expected to supply portable equipment used outdoors was a requirement of both the 15th and 16th editions, it is unlikely that an external non RCD protected socket complied.

In such a situation I would use code C2 for all instances where RCD protection is now required.
 

Reply to Test failed due to missing RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
669
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top