Hi All
Recently joined the forum to ask for some information.
I recently bought a flat to let. I was advised by the letting agent to get the electrics tested, although not a legal requirement. The test was carried out by their electrical contractor. He failed the test due to the fuse board not having an RCD fitted. The fuse board is the original board fitted in 2003 when the flats where built. There has been no mods or circuits added to the system and everything is working as it should. I paid £348.00 for the test and the RCD to be installed. I have since been told that the test should not have failed due to the lack of the RCD. Have I been stitched up.
Any comments gratefully recieved

Peter
 
It is this type of lazy approach to sparking that bothers me. Itnis not a given fact that just installing RCDs ‘make it safer’.

The ‘RCD everything’ approach without no design or thought behind it is not what we ahould be doing. We could just say ‘wire everything in SWA makes it safer’. Why do we not do this? Because we need to ise our skill and interpretation to determine if these extra precautions are actually needed.

In this instance a safe installation has been made less safe by installing an ‘up-front’ RCD which is not to Regs.
What a load of rubbish.
Sorry @sparksburnout ... Totally misread your post.. :tearsofjoy:
Thanks for the clarification @Risteard
Go and stand in the corner for 30 mins.
 
It may have improved the protection/safety aspect but its the danger that it could cause with the whole flat being in darkness to the occupier. How have a conclusion also come about that this is a ground floor flat?and sockets would be used for outside.
 
the danger that it could cause with the whole flat being in darkness to the occupier.
It may not be ideal, but realistically what danger do you envisage. If there is a power outage is the installation dangerous?

If there is an identifiable danger with failure of the lighting then why has emergency lighting not been installed?
 
I don't know, why didn't they fit RCBO'S?
Obviously I can't answer that, but possibilities are availability for the particular DB, or cost, or time it would take to source them amongst others. There's really not much point in me guessing why it was done the way it was.
 
I really don't get how anyone could imagine that having an up-front RCD in this instance could possibly be more dangerous than the worry of "all circuits being lost", as if it is some kind of regular occurrence or even that much of a disaster if it happened. I would think most people with a bit of common sense would have one of those old fashioned things called a TORCH for such things, you know, like if there was a power cut. I think some folks have some sort of phobia of losing all the power, how often does it happen??
 
With rented property and the chance of a Tennant plugging in something like a cheap usb charging plug for example. Having no RCD protection is a risk if the worst was to happen. I won't pass rented property with no RCD protection. The risk to the landlord and the electrician who signs the cert. Is just to high. You will find people who will do it with an observation. That's up to the individual.
 
Was not aware the Regs are now pick and mix.
When did that happen?

How about instead of doing a half arsed job, you do the job properly and comply with all the Regs, not just some of them?
In fairness the Regs do not state that an installation may not be protected by a single RCD. It is one interpretation of a particular Regulation which generally leads to that conclusion.
 
I don't agree. He has improved the safety of the installation. Certainly it would have been better to use multiple RCDs, but it's not correct in my view to state that he has made things worse by protecting the installation with an RCD.

Front-end RCDs don't tend to trip very often - normally only when there is a fault.

But it is not to BS7671 to install a single up-front RCD.

An installation designed to meet BS7671 and not need additional RCD protection is no less safer than putting an RCD in. Sometimes I think the opposite is true. For example I woukd consider cables concealed in metal conduit in the walls safer than cables not in metal conduit but have an RCD as additional protection.
 
"Due account shall be taken of the consequences of the operation of any single protective device."

That is not a prohibition. It does require the consequences to be assessed, however.
 
It’s not only one Regulation, and why are they only interpreted to mean something other than what they say?
How exactly does changing multiple separate circuits with individual protection to multiple separate circuits protected by a single device minimise inconvenience in the event of a fault?
How does doing such facilitate safe inspection, testing and maintenance?
How does it reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor (PE) currents not due to a fault?
How does it allow for separate circuits not being affected by the failure of other circuits?
 
Only someone trying to justify a get around would say that.
Not at all - it's what someone trying to have a factual debate on the particular merits and demerits of this approach would say. As I have stated numerous times it certainly isn't an ideal approach, but is nonetheless a safety improvement for the electrical installation.
 
Surely, if installed in 2003, this CU ought to have had a 30mA RCD for the Socket outlets only if nothing else to conform to 16th Edition? Or is my memory sketchy?
That would only be the case, if it could reasonably be expected that sockets would be used to supply portable equipment outdoors.
An upstairs flat with no garden and no off street parking, would not normally have RCD protected sockets.
 
"Due account shall be taken of the consequences of the operation of any single protective device."

That is not a prohibition. It does require the consequences to be assessed, however.

I was thinking more of 314.1:

Every installation shall be divided into circuits, as necessary, to:

(i) avoid danger and inconvienience in the event of a fault.


And

314.2:

Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.
 
Not at all - it's what someone trying to have a factual debate on the particular merits and demerits of this approach would say. As I have stated numerous times it certainly isn't an ideal approach, but is nonetheless a safety improvement for the electrical installation.
Whether such an approach improves safety, is debatable.
What is not debatable, is that both 314.1 and 314.2 require circuits to be separate.
 

Reply to Test failed due to missing RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
404
  • Question
Yes good point, I've had this situation in the past, never give it a thought in response to the OP!
Replies
8
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
841
Hi, did you decide to upgrade your test meter? If so, how are you finding it?
Replies
1
Views
702
  • Question
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
    • Like
Replies
15
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks