What if , right, you've already got 50m of 2 core and you've promised to do your cousins garden lights cheap? If you're worried about degradation , WD40 doesn't hurt on the armour, a liitle bit of mastic etc. And you would have to be especially gifted to cut through the armour enough to give you an earth free path to a live conductor without getting enough earth path through your spade or is it ceramic? I'm only messing!!
 
What I have been doing, and has been accepted by many companies I've been testing for, is I write "SWA" in the cpc column of the test sheet instead of a conductor size.
In the cable type coloumn I write "F" for PVC/SWA or "G" for XLPE/SWA.

It is good practice to use a 3 core SWA now and utilise one core for a cpc, but I dont think there is anything wrong with using the armouring of a 2 core cable for a cpc as long as it is fit for purpose, ie check old cables for signs of excess corrosion.

If someone was to cut the cable, and the blade was to go through the armour into the live conductor first before going into the cpc a dangerous situation would occur. So you need to bond the armour of a 3 core cable to provide the earth path, even if your not using it as the actual cpc.
 
I take your point, but if you run a SWA underground (say 3 core and each core is used as a line conductor) and someone goes though that with a saw, (seen it a few times when people have foundations dug out for a conservatory) then that cable will still be live, not trip the Protective device and becomes a hazzard to the poor bugger you grabs the end of it (if not already had a shock from saw). Where as if the Armour was earthed then the protective device would trip preventing the risk of shock.

The seperate earth would only provide an earth at the other end, but so does the armour. if the ends are terminated properley then there shouldnt be any moisture ingress, and the cable (inc earth continuity) should has as long as the installation

you've got this totally wrong mate, the armouring MUST have a good connection to earth, through the glands, which, if not connected directly to earthed metalwork, then you are required to ensure continuity must be maintained by using a brass banjo. (I also like to use serrated washers to dig into any metal casing to give a good connection).

what the discussion is about is; wether the armourings can/should be relied on for the only means of earthing, armourings and the glands can be considered exposed conductive parts which also requires they be earthed regardless.

also you quoted "if the ends are terminated properley then there shouldnt be any moisture ingress"

shrouds are not always perfect, and if connected outdoors any bangs or bumps could expose the armourings to the elements. but the consideration should not just be fo the ends, what you'd have to consider is, if someone did give the cable a clout it doesn't always take a lot to remove a bit of the sheathing, the tiniest nick could let in water and cause the armourings inside to deteriorate. i've changed loads of SWA which have had water ingress regardless of how good the connections were at the gland
 
I'm with the flukey dude. you can only do an install to the best of your ability. you have no way of knowing what some eejit is going to come and do to your lovely tidy install. If the book says "yes" then someone else has made the decision of wether it's acceptable or not. Obviously a bit of common sense needs to be applied. !
 
i guess it's each to their own, but i don't think i'd be running SWA without a dedicated CPC, just what i was taught i guess
 
The electricity board relay totally on the armour in a TN-S system and TN-C-S sysyem. Regs say its fine so really cant see the problem with using the armour as the sole means of earthing.
 
ive seen allot of sparkys write (sheath) where you would normally write the size.makes sense to me as the armouring is a sheath.
 
HI,
The nic have a guide for this within one of their books.I had the same problem recently on a periodic test.The flats were built early 1980s and 2 core swa was used.It turns out that 16mm 2 core swa is equal to a 10 mm earth on the armour.I agree we would not rely on this now but my loop readings were fine so could not fault it.I also contacted the manufactors of the swa who confirmed the same.
 
NO NO NO - i believe you are very wrong there!

the armouring is not designed to be relied on as an earth connection!

the armourings reason for being there is to offer mechanical protection, end of - the earth connection is a benefit. the armourings are there to try and protect the cable from being cut through, which is why you use ARMOURED cable! armour is armour, earth is earth

i'm not saying it can't be used, it is (i believe) good practice to ensure if there is no core to be used as an earth then a seperate earth will be run. the csa of the armourings meets the requirements of the regulations (unless you start using single cores or two core SWA with conductor CSA's of greater than 120mm)

whilst it may be adequate on installation, with 5 years of degredation (depending on the environment) it could easily break down/rust at the glands or any breaks or water ingress into the pvc sheath.

if it's possible i'd always run a seperate earth, and it is in most circumstances i think reasonable to do so

I'm a bit confused
Two different views in two posts, So do you always run a separate CPC or do you sometimes rely on the armour even though you appear so against it
 
The selection and erection guidance note (don't have it here so can't remember specifics) tabulates most pvc and xlpe armour sizes and also states if the armour is adequate for use as the cpc without a parallel cable.;)
As far as I'm concerned if the CPC is run as a core within the cable I'll bond one end of the cable with a bolt and banjo, if the armour is to be used I'll banjo it and flylead it BOTH ENDS with a cable of a suitable size for a cpc so for the sake of argument 6mm/2.5 is standard T&E then a 2.5 single will be adequate as a flylead for a 6mm SWA.
 

Reply to Testing SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
500
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

totally agree
Replies
12
Views
2K
You would treat it as a TT installation.
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top