Thermo dynamics for hot water that runs off atmosphere | Page 12 | on ElectriciansForums

Discuss Thermo dynamics for hot water that runs off atmosphere in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Do you mind me asking what methodology they used?

Did they test it with varying wind and solar input levels, or just in static air at different air temperatures?

If the latter then I'm not surprised it didn't come out too well.

The system was installed with the panel on the roof facing south, the hot water was taken from the cylinder two ways (different tests) the first using a timed release of hot water (very wasteful) to simulate domestic usage the most taken from a 280L cylinder was 100 litres at a time.

The second was using a system link which allowed it to dump the heat into their central heating system.

The entire procedure lasted over six months.
 
Today's observations on a 200l cylinder:

Ambient - 2.5 deg C
Compressor draw - 3.6 amp
Water entering - 8 deg C
Raise - 24 deg C (to 32)
Time - 90 mins

I did check today if the immersion was on during initial warm up. It wasn't.
 
Today's observations on a 200l cylinder:

Ambient - 2.5 deg C
Compressor draw - 3.6 amp
Water entering - 8 deg C
Raise - 24 deg C (to 32)
Time - 90 mins

I did check today if the immersion was on during initial warm up. It wasn't.
I get that as being a COP of 4.3ish, depending on what the grid voltage was (figure given is for 240V / 864W / 1.3kWh electrical input, 5.58kWh heat required to heat 200l of water by 24 deg), and if that was the ampage for the entire time.

That's none too shoddy. What was the weather like?
 
I thought it would have been windy, or sunny.

obviously this would be at the point where the heat pump was operating more efficiently due to the lower output temps, and would presumably drop off the COP as the output temperature rose to 55deg, but still a COP of 4.25 at 2deg external air temp is pretty good.
 
Re: info

I have read all posts in this thread with great interest. I am about to chuck away my combi boiler and install a 400 litre thermal store to keep up with increased central heating and DHW requirements. (i am doubling the floor area of my property and adding a further bathroom). The thermal store will be heated by various sources. A mains gas boiler, a multifuel stove and also an electric heat source powered by effectively free of charge excess electricity produced by my 4kw solar PV array and diverted using an immersun unit. I could simply use an immersion heater, but thermodynamics has caught my eye. I can buy and install a single panel thermodynamic system myself for around ÂŁ2000 (including F gas installation). As the electricity is 'free' and looking at the claims for thermodynamic systems i think the investment could well be worth it. Does anyone have any views on this idea, any input would be gratefully received, thanks, Michael.
 
Interesting. Can you explain further why mixing all the the forms of heating into one store.
How will you combine the thermodynmaics system into the thermal store?
Where abouts are you in East Midlands. Sorry about or the questions just interested
 
Interesting. Can you explain further why mixing all the the forms of heating into one store.
How will you combine the thermodynmaics system into the thermal store?
Where abouts are you in East Midlands. Sorry about or the questions just interested

I need a big thermal store as i will have 18 rads and 5 underfloor circuits and 3 bathrooms to service. I didnt want to heat it using just gas as i am trying to keep running costs down. I have a steady supply of free wood for the multifuel stove (winter) and the free surplus from the PV (summer) to this end. If i use thermodynamics it will be via an indirect coil in the bottom of the thermal store (one usually used for solar thermal). The store needs to be 75C at the top, the bottom will run cooler as it is where the return pipes from the heating circuits come back in. I'm hoping that the advertised 55C will work at the bottom of the store....... I am based near Ashbourne, Derbys.
 
400 litre thermal store is way too small. This will be little more than buffer tank. This needs to be correctly sized for the job in hand and the range of heat inputs. Immerses need to be correctly located so it can be used for hot water only in the summer. You will probably find you need a tank of at least 2000 litres. Are you planning to use an internal heat exchanger or an external plate heat exchanger for hot water?

with regard to thermodynamics, read all the threads on this site before making a decision. They are currently excluded from MCS and RHI. You could be far better off with traditional solar thermal.
 
400 litre thermal store is way too small. This will be little more than buffer tank. This needs to be correctly sized for the job in hand and the range of heat inputs. Immerses need to be correctly located so it can be used for hot water only in the summer. You will probably find you need a tank of at least 2000 litres. Are you planning to use an internal heat exchanger or an external plate heat exchanger for hot water?

with regard to thermodynamics, read all the threads on this site before making a decision. They are currently excluded from MCS and RHI. You could be far better off with traditional solar thermal.

I agree, just one point though, if Micheal P has gas into his heatstore, then will he still be eligible for the RHI?
I believe it is a good idea to have several heat sources to a heatstore although it can make it a little difficult to set up, as ideally at any point in time you want the "free heat" to be used first, IE logs in your case, however your "free heat" will change daytime/nighttime, winter/summer.
Complex but possible, get it right and it would be fantastic.

The jury is still out on thermodynamics, as an addition to your heatstore, personally, if it was in my budget I would give it a go, but I would not rely on it, but in twelve months time you may be telling us great it is.
 
i thought thermodynamics had to be on its own cylinder as it works with F gas

I was thinking of using one of the magic box systems which basically outputs the water at 55C from the box. Feeding this to an indirect coil distances the F gas from the thermal store. I hope i am correct?
 
400 litre thermal store is way too small. This will be little more than buffer tank. This needs to be correctly sized for the job in hand and the range of heat inputs. Immerses need to be correctly located so it can be used for hot water only in the summer. You will probably find you need a tank of at least 2000 litres. Are you planning to use an internal heat exchanger or an external plate heat exchanger for hot water?

with regard to thermodynamics, read all the threads on this site before making a decision. They are currently excluded from MCS and RHI. You could be far better off with traditional solar thermal.

The hot water is created indirectly by running mains pressure cold thru the store via a high recovery stainless coil. See eco-equipped.com for the products. I will use an EC solar 400 with an add on to run UFH indirectly. I cant use solar thermal as the only roof available is north west facing.....not worried about RHI payments, i just thought that thermodynamics might be a better way of using the excess from the PV array
 

Reply to Thermo dynamics for hot water that runs off atmosphere in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
239
People who claim to be plumbers... and tilers... New bath fitted and the drain is accessible from the side and there are isolating valves on the...
    • Like
Replies
0
Views
217

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top