Thoughts on this set up | on ElectriciansForums

Discuss Thoughts on this set up in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Jan 29, 2021
Messages
4
Reaction score
0
Location
Kinross
This is supplying a small commercial set up. SWA is only 16mm and the isolator is rated at 100A. Earth cable between MET and SWA is only 10mm.
How would you code it? Having a brain fart and thought I'd seek other opinions.
[ElectriciansForums.net] Thoughts on this set up

[ElectriciansForums.net] Thoughts on this set up
 
Last edited:
Poor workmanship certainly the Swa needs proper protection KMF 60 amp
2Core not ideal the armouring, when terminated correctly, may be sufficient for CPC, but not for Main Bonding Protective Conductor😎
 
I’d say there’s been a proper set up before… with the gland into a box.. seeing that there’s a shroud there.

Also old screw holes in the back board suggested there’s been old equipment removed…. Like an older style meter.

Agree on C2 for unsheathed cables…. It may be in a lockable enclosure ( hopefully it’s got a door and is lockable!) but it’s available to untrained personnel to open up and read the meter.
 
The unsheathed cables are definitely a C2.
The lack of overcurrent and fault protection is a C2 as well.
The G/Y cable may be OK. It depends on what the earthing system is in the commercial unit.
D
 

Reply to Thoughts on this set up in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
105
  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
422
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
370

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
462
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top