Coincidently I'm just looking at something along these lines at this very moment. Scenario is I need a 298 amp flc 3 phase supply to run a compressor but the panel board is obselete and I'm struggling to get hold of a 320 amp mccb which can be adjusted down to 300. The one I can get is 400 amp, adjustable to 320, but my cable calculations came out with 95mm with a max load of 304 A.
I have 2 possible options, 1 is to upgrade the cable to 120mm which I don't want to do if possible due to cost and slightly harder to terminate into connections etc.
Other option is rather than an isolator at the compressor end, use a fuse switch and 300A fuses to limit overload current.
What do you reckon? It'll undoubtably come down to cost in the end
P.s option 3 would be a new panel board but the implications of shutting the plant down are huge
I have 2 possible options, 1 is to upgrade the cable to 120mm which I don't want to do if possible due to cost and slightly harder to terminate into connections etc.
Other option is rather than an isolator at the compressor end, use a fuse switch and 300A fuses to limit overload current.
What do you reckon? It'll undoubtably come down to cost in the end
P.s option 3 would be a new panel board but the implications of shutting the plant down are huge