Coincidently I'm just looking at something along these lines at this very moment. Scenario is I need a 298 amp flc 3 phase supply to run a compressor but the panel board is obselete and I'm struggling to get hold of a 320 amp mccb which can be adjusted down to 300. The one I can get is 400 amp, adjustable to 320, but my cable calculations came out with 95mm with a max load of 304 A.

I have 2 possible options, 1 is to upgrade the cable to 120mm which I don't want to do if possible due to cost and slightly harder to terminate into connections etc.

Other option is rather than an isolator at the compressor end, use a fuse switch and 300A fuses to limit overload current.

What do you reckon? It'll undoubtably come down to cost in the end

P.s option 3 would be a new panel board but the implications of shutting the plant down are huge
 
Short run of 120mm to a new small sub board where you fuse down to 300A and then run from that to the compressor in 95mm? I don't know industrial electrics so I'm just going from first principles. And hopefully learning as I go.
 
If the full load current is 298A and your cable's ccc is 304A then the only option IMHO is a fused switch (as opposed to a switch fuse) at the load end providing your supply cable is protected against fault current in accordance with section 434.
 
If the full load current is 298A and your cable's ccc is 304A then the only option IMHO is a fused switch (as opposed to a switch fuse) at the load end providing your supply cable is protected against fault current in accordance with section 434.

That's what I'm leaning towards, I thought I said fused switch rather than switch fuse.

No space to fit a sub board and it would work out costly, MEM are already taking the p*** with the MCCB so I'll be looking for a different brand fused switch to the glasgow I was going to get.

I'll be having a look at the fault current calculation tonight, and looking on ebay for a MCCB!

Thanks for the advice, any opinions on a fused switch with plenty of room to terminate cables? looking like I'll need a couple of spreader boxes.
 
It's the fuses I'm struggling with. Looks like they jump from 250 to 315.

I might have to postpone the job until I can get a 320 a adjustable mccb .

Failing that bite the bullet and go with 120mm cable

I fully expected to pay that for the fused switch but they are asking 1300 + vat for an mccb !
 
Each 20A load would need a 20A fuse to protect the 2.5, surely without this then is one of the loads increased through whatever reason, the 2.5 would melt well before the 100A tripped.
I'm with shanky887614 on this one.
 

Champion , there's the job sorted. As luck would have it I've managed to locate a 320a Mccb so no need for them now but I have a back up plan in case it goes before I get the order .

Glad I had these problems in a way cos it does no harm to get the grey matter working and do a few calculations to solve a problem . Thanks for the help, much appreciated
 

Reply to Thoughts please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K
  • Article
This is an RSS feed of thread: ADVICE for young plumber required please staffs/midlands Content of the thread: hi all, posting on behalf of my...
Replies
0
Views
230

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top