Just did a three phase consumer unit, tested insulation and continuity before commission tested three phase in correct order. When I switched on it sparked and took out l1 and l2 fuse, incomer has two faulty lock screws at top apart from that any other ideas ?
re above: Really by todays DNO's standards you and tenants should have 24hrs access to the service cable and all meters switch fuses for sub mains etc. The reason is if any of the tenants have any problems tenants / electrician can get to all electrical equipment. Like you just experienced, tenant to basement out, so you couldn't complete your work. Glad you found problem though.
I think that the DNO should of been consulted before work started and the service intake position resited. How are all flats being metered?
This isn't correct if wired correctly with submains to each flat CU and discrimination correct then Tenants access isn't required, only a submain cable fault would loose power to the flat and this would require a competent Electrician anyway.
As regards to Metering if the design is correct the Landlord will take all individual Meter readings and pass the reading with bill to the tenants... if however a tenant disputes a reading he allows them access to confirm. The Tenant will have witnessed the initial meter reading when they took tenancy.
Only access needed maybe if a tenant is on a pay as you use of which necessary arrangements are made. I see no reason for tenants to have access to said area if it is designed correctly.
Dno has been out and want money to move the head. The flats are all metered from basement and have tails running to consumer unit. The two flats are sharing a db in hallway as landlord does not want to spend any money not an ideal situation.
Reply to Three phase question in the UK Electrical Forum area at ElectriciansForums.net
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Recommended Sponsor News
Hi everyone,