I beg to differ.2.5 cable can take a max of 27 amps if clipped direct.23amps in a wall or 21 amps above a plasterboard ceiling with insulation.Putting a 2.5 on anything bigger than a 20amp breaker would be madness.Personally i would put a 16amp breaker feeding it.If you wish to back up your claim then please quote the relevant BS7671 number.
I shall take the challenge :). I haven't got the BYB with me so I cant give you the exact page but if you take a look at appendix 15, reg 433.1.5, fig 15A and read under the 'unfused spur' title it will say:

"An unfused spur may be
connected to the origin of the
circuit in the distribution board."

If you think about it, it's exactly the same as spurring of a ring. As Ian has said, it cant be overloaded as the CCC is 27A clipped direct and fault protection is easily met with a 32A MCB. Plus.... It is in the regs as above.
 
Last edited:
No the breaker would be oversized it has nothing to do with recent changes.
Hi , I had one 32a mcb spare in the main board and needed 2 separate 16a mcb to supply 2 catering toasters.Not domestic.
So maybe it was wrong . Maybe it is time to bow out .
Thanks for your input
 
I get the ring final spur but why are people justifying, creating scenarios pushing this cable size to its limit when in reality they wouldn't do it.
Because this is a forum, and they can. ;)
But undersizing the cable then using the regs to back up the decision is pointless if you ask me.
 
I shall take the challenge :). I haven't got the BYB with me so I cant give you the exact page but if you take a look at appendix 15, reg 433.1.5, fig 15A and read under the 'unfused spur' title it will say:

"An unfused spur may be
connected to the origin of the
circuit in the distribution board."

If you think about it, it's exactly the same as spurring of a ring.

I said the same or very similar in post #13 HHD, in your defence. :)
 
"An unfused spur may be
connected to the origin of the
circuit in the distribution board."

If you think about it, it's exactly the same as spurring of a ring.

Your original post didn't mention spurs.You said you could run a double or single socket directly off a 2.5 fed from a 32amp breaker.in that specific case i would say thats unacceptable.If you were wiring the socket from scratch you would fit a 16amp breaker to feed the double or single socket.
 
I shall take the challenge :). I haven't got the BYB with me so I cant give you the exact page but if you take a look at appendix 15, reg 433.1.5, fig 15A and read under the 'unfused spur' title it will say:

"An unfused spur may be
connected to the origin of the
circuit in the distribution board."

If you think about it, it's exactly the same as spurring of a ring. As Ian has said, it cant be overloaded as the CCC is 27A clipped direct and fault protection is easily met with a 32A MCB. Plus.... It is in the regs as above.
Why would you install a radial, not a spur from a ring final in the same manner. Pointless exercise.
 
Your original post didn't mention spurs.You said you could run a double or single socket directly off a 2.5 fed from a 32amp breaker.in that specific case i would say thats unacceptable.If you were wiring the socket from scratch you would fit a 16amp breaker to feed the double or single socket.

Come on Bob, admit defeat like a man :)
What else is a spur if it's not fed from a 32a MCB feeding a single or double socket?
Go on Bob, I've been wrong a hundred times and am happy to put my hands up when defeated... It feels good!
 
I said the same or very similar in post #13 HHD, in your defence. :)

Sorry Dave, didn't see that! Thankyou :)

I'm off to see a very pretty new girlfriend now so shall say goodbye for now.
 
Come on Bob, admit defeat like a man :)
What else is a spur if it's not fed from a 32a MCB feeding a single or double socket?
Go on Bob, I've been wrong a hundred times and am happy to put my hands up when defeated... It feels good!
Well it isn't a spur, it is a radial there is no ring final.
 
Sorry Dave, didn't see that! Thankyou :)

I'm off to see a very pretty new girlfriend now so shall say goodbye for now.

Oh no you're not, get back here and argue about the rights and wrongs of sticking 2.5mm cable in a 32a mcb, that will go round and round and round and round and round until we all agree to disagree.
 
Sorry Dave, didn't see that! Thankyou :)

I'm off to see a very pretty new girlfriend now so shall say goodbye for now.

She's not new, he's had her for ages and that's why he was quiet the latter part of last year. How do you spell oooeeeooo @Pete999 is good at spelling noises!

@Sparkhe, don't be down. You have 30 years of experience to give. If you need to catch up since the 16th then hang around on here and read through the archives. There is the 17th 2382-15 from city and guilds that you would ace then you'd be back on track.
You've probably forgotten more than half of us know, although listening to us bickering about 2.5 Spurs will probably make you want to leave the game anyway.
Hoping to hear more from you, get involved and have a banter!
Respect, Rob
 
She's not new, he's had her for ages and that's why he was quiet the latter part of last year. How do you spell oooeeeooo @Pete999 is good at spelling noises!

@Sparkhe, don't be down. You have 30 years of experience to give. If you need to catch up since the 16th then hang around on here and read through the archives. There is the 17th 2382-15 from city and guilds that you would ace then you'd be back on track.
You've probably forgotten more than half of us know, although listening to us bickering about 2.5 Spurs will probably make you want to leave the game anyway.
Hoping to hear more from you, get involved and have a banter!
Respect, Rob
 

Reply to Time to call it a day in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
184

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top