G
Gardner
Are earth rods or earth electrodes required for TN-S supply?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss TN-S Earthing in the UK Electrical Forum area at ElectriciansForums.net
If there is an earthing system of TNCS or TNS then the supply earth is provided by the distribution network operator, it is not permitted for us to create a TNCS system by making a N-E link.
The earth must either be supplied from the public supply system by the DNO or, if an earth is not provided by the DNO, then we can install an earth electrode.
If there is no earth provided at the installation then one can request an earth provision from the DNO, but they do not need to provide one, e.g. if the network conditions are not suitable or the installation may present danger with a TNCS system.
What do you mean the DNO will provide an earth? My understanding is the DNO will either proved 3 wires (TN-S), 2 wires with the incoming neutral bonded (TN-C-S) or 2 wires with neither conductor supposed to be earthed at the premises (TT supply).
Or you mean the N-E link must only be made by the DNO and not the electrician?
That's the one!!
So if lets say I had a home with no rebar in the foundation, and the water line coming in was plastic with no gas on the property, I can just run a jumper from the neutral to the main earthing terminal and be code complaint?
An earthing electrode only serves the function of fault clearing as in a TT network?
Ok that make sense now. Thanks Now with that said, this equates to an electrician not being allowed to touch the incoming service head as that is where the N-E bond is made?
The N-E connection is made at the substation. The DNO cables will have a CNE conductor in them which is connected to earth electrodes periodically. The DNO will either connect your earthing conductor to their CNE terminal or remove a knockout in the side of the head which allows you access to one of the terminals in the CNE block so that you can connect your earthing conductor.
CNE? IS that an SWA cable shield?
CNE? IS that an SWA cable shield?
Combined Neutral and Earth
OK, that would make it a MEN system.
In a TT system do DNOs usually earth the neutral repeatedly or only at the 11-400Y substation? Of course this would not matter at the customer but just trying to get a sense of whats going on.
OK, that would make it a MEN system.
In a TT system do DNOs usually earth the neutral repeatedly or only at the 11-400Y substation? Of course this would not matter at the customer but just trying to get a sense of whats going on.
Have a look at this attached pdf,
That clears up a lot! Thanks
One question that stands out. One page 3 where a TN-C-S system is shown it says "Additional source electrode" What do they mean by that? Is this electrode part of the DNO or electrician supplied connected to the MET?
Reply to TN-S Earthing in the UK Electrical Forum area at ElectriciansForums.net