Evening All. I am about to carry out a domestic rewire to a property which has TNS earthing. The DNO has recently done a bit of work installing a new isolator, smart meter, contractor for Econ 7 switching etc and tidied up their end of things a bit. There is no MET at present and everything (Main bonding and main earth) seems to have been earthed at the incoming sheath. Pity DNO didnt install a new MET but they didnt.

Am I allowed to connect to their sheath directly or should I ask them to provide a MET and the 16mm from this to their sheath? I would prefer to have a MET, just looks tidier than the connection direct to the sheath as currently made in the attached photo.

[ElectriciansForums.net] TN-S No Main Earth Terminal
 
Last edited:
That wouldn't normally happen. Usually, when only a single phase supply is needed, only a single phase cutout is installed. Before I became a trainer, I worked in metering for over tewenty year and we had a large number of 'four in a block' types of flats in our area. They usually had a three phase supply in one of the flats feeding submains. The flat with the incomer was never fed from L1, always one of the other two. This meant that to get at the neutral cover, two flats had to be disconnected. It was infuriating and unnecessary.
 
That wouldn't normally happen. Usually, when only a single phase supply is needed, only a single phase cutout is installed. Before I became a trainer, I worked in metering for over tewenty year and we had a large number of 'four in a block' types of flats in our area. They usually had a three phase supply in one of the flats feeding submains. The flat with the incomer was never fed from L1, always one of the other two. This meant that to get at the neutral cover, two flats had to be disconnected. It was infuriating and unnecessary.

That sounds like bad design/planning on the original installers part.

There are a lot of houses around here with three phase supplies in PILC with only one phase used, and a lot of them are on very old cutouts
 

Reply to TN-S No Main Earth Terminal in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top