A

AdamGiguere

Hi there

Testing at origin of a domestic property, I have found:

L-N: 0.44 Ohms
L-E: 9.89 Ohms

I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)

My concern is they don't seem to have checked the reading between L-E......

Anyone know what could be the cause of this? MET connections are tight and in good condition....

Many thanks in advance.

Adam

[ElectriciansForums.net] TNCS High ZE at origin
 
The only cable I've installed is the 16mm T&E, everything else is existing...
To me that is very worrying that you are carrying out electrical works on other people's properties.
 
There has been two previous electricians as well who have not picked this up.

I'll be upgrading to a switch fuse as advised, but sparkychic what's the deal with existing then surely it all needs upgrading to switched fuses regardless of it being existing....

Westward I'm learning everyday.
 
So going forward such as today, I'm running 6mm swa from meter intake to outside garage.

I'll run the swa into a metal consumer unit in the garage.

At the meter I will upgrade to a double pole Henley block and have the swa on a 60amp switch fuse for protection of the 15m run.

I'll update the tails from the Henley block to existing fuseboard which is just next to the meter.
 
As previously stated, using an MCB can lead to discrimination issues under fault conditions.
Many thanks once again.

I understand on this clearly now.

I can take tails from the meter into my 100amp switches fuse which I'll install to the right of the meter at high level in the meter cupboard.

From the sf isolator I'll run tails to the Henley block which supply's the three feeds.

Also I'll use containment to protect and neaten the cables inside the meter cupboard
 

Reply to TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top