A

AdamGiguere

Hi there

Testing at origin of a domestic property, I have found:

L-N: 0.44 Ohms
L-E: 9.89 Ohms

I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)

My concern is they don't seem to have checked the reading between L-E......

Anyone know what could be the cause of this? MET connections are tight and in good condition....

Many thanks in advance.

Adam

[ElectriciansForums.net] TNCS High ZE at origin
 
Ok but if my EFLI is within the parameters then I should achieve my disconnection times regardless whether they are on switch fuses right?

They are on double pole isolators via their main switch on the DB....

Slightly confused in this regard
 
The service head fuse isn't there to protect your equipment, it's only there to protect the suppliers equipment and cabling.

So your protection only starts at the consumer unit. If that's 10m away from the metering location, that's 10m of effectively unprotected cable and you have no guarantee that a fault on that cable will be disconnected quickly under fault conditions.

Hence, runs longer than 3m require the presence of a suitably rated protective device... to protect the distribution cables that supply power to the remote consumer units.
 
Thanks Spark Chic!!!

Understood, what switch fuse would you advise to use that would be small enough to fit in this cupboard? as I do believe the tails at right end are also feeding cables with a run longer than 3 meters so I'd really need all 3 runs connected to individuals 60amp switch fuses
 
Within the meter cupboard, these are suitable:-

80A Double Pole Fused Switch | ElectricalDirect - https://www.electricaldirect.co.uk/product/80a-double-pole-fused-switch-324279

In the house, you'd really need one in a metal enclosure to comply with the switch gear should be in non-flammable enclosure regulations. These are generally bigger. But from the looks of the meter cupboard, it's a bit tight already. If you could re-route the cables, then providing you can get the switch fuse within 3m, you could put them elsewhere and supply them with suitably rated meter tails.
 
The 3m limit is widely regarded as the maximum acceptable distance and it's the answer most people get when they enquire with the various distribution network operators.

You won't find it in BS 7671 because it's part of the DNO network design guides.

The best thing to do is measure up and have a chat with the DNO. My DNO is Western Power Distribution, their limit is 3m, but they don't seem to police it as I've worked on several properties which breach it. One place I've been to built in 2007 has tails over 10m long and no switch fuse, another has a 16mm T+E running about 25m.
 
Right i see!

The DNO have on this property don't seem to be policing this here.

They've not advised this work should be done.

If BS7671 doesn't stipulate and DNO is just a guide is this absolutely necessary?

Great info by the way - this forum is just what's needed!
 
Within the meter cupboard, these are suitable:-

80A Double Pole Fused Switch | ElectricalDirect - https://www.electricaldirect.co.uk/product/80a-double-pole-fused-switch-324279

In the house, you'd really need one in a metal enclosure to comply with the switch gear should be in non-flammable enclosure regulations. These are generally bigger. But from the looks of the meter cupboard, it's a bit tight already. If you could re-route the cables, then providing you can get the switch fuse within 3m, you could put them elsewhere and supply them with suitably rated meter tails.
Something like this would work if it combined the 3 sets of cables that are in there.

Could I not put a small 3 way board in there, as rerouting the cable would not be ideal, tenant wouldn't want to spend the money for the time it would take etc...
 
Is it absolutely necessary?

Well, if you want to ensure the safety of the users of the installation and the property that contains it, then the answer should be yes. The DNOs don't police it because their responsibility ends where the tails leave the service head to go to the meter. From there up to and including the meter, the responsibility sits with the energy supplier and after that, it's the customers responsibility. The DNO can only advise.

Potentially yes, you could install a small board, but make sure you use fuse carriers, not MCBs or similar as if you don't you could have problems with discrimination under fault conditions.
 
Is it absolutely necessary?

Well, if you want to ensure the safety of the users of the installation and the property that contains it, then the answer should be yes. The DNOs don't police it because their responsibility ends where the tails leave the service head to go to the meter. From there up to and including the meter, the responsibility sits with the energy supplier and after that, it's the customers responsibility. The DNO can only advise.

Potentially yes, you could install a small board, but make sure you use fuse carriers, not MCBs or similar as if you don't you could have problems with discrimination under fault conditions.

Thanks, what fuse carriers fit in the new wylex metal boards?
 

Reply to TNCS High ZE at origin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top