I would bed to differ. The last TT system we tested was 0.73 and that was only a single rod.

Although I do agree it is unlikely to be ever able to prove a permanently and reliable Zs on a TT system it does loosen the requirements a little and in this case a 500mA RCD would be more than enough.


Think the installer may have hit an earthed source . Done loads of TT systems, to get an RA of 0.73 ohms with one electrode I’d need to see it to belive it and then see it again
 
Think the installer may have hit an earthed source . Done loads of TT systems, to get an RA of 0.73 ohms with one electrode I’d need to see it to belive it and then see it again
Had one the other week and it's been bone dry for a while...

[ElectriciansForums.net] TT and RCD protection
 
Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.

I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?

Are you talking domestic?
I've worked in industrial units, multi rodded, maybe nested with Ra of well under. You'd think they were TN, until closer examination.
 
Last week on a new install we put 5 rods down into what seemed like sand to achieve an Ra of 132.4 ohms. We only stopped at 5 because we ran out of rods. This week we will be digging a new trench from the incoming supply building to an area of much firmer ground so that another rod will provide a more acceptable result.
Incidentally, 400v supply leaves the meter and hits a distributors 4 pole switch, then a 4 pole 100mA/100A Time delayed RCD. Splits 3 ways to 2x 3P+N switch fuses for distribution to remote buildings and a local 1P consumer unit for construction supply, treatment plant & local lighting.
 
I would bed to differ. The last TT system we tested was 0.73 and that was only a single rod.

Although I do agree it is unlikely to be ever able to prove a permanently and reliable Zs on a TT system it does loosen the requirements a little and in this case a 500mA RCD would be more than enough.

must be all that fake tan lotion soaked into the ground.
 
Quick question guys im moving my board 5 metres. Currently on a tt system but within the next few months will have western power convert it to tncs. But in the mean time would it be ok to put up just a kmf switch or a time delayed rcd before the tails?
 

Reply to TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
596
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top