Hi all, I would like to put a second earthing rod at a garage that is a little remote from the house, so as well a using the house earthing the garage would have the second rod, this would also add a second earthing route for the house, Is this permissible and can anyone see any problems occurring . Sidey
 
Hi Richard, Thanks for your reply, I had done the relevant impedance calculations and could see no problems but needed a second view in case I had forgotten something. If you have already had this reply it's because I'm just getting to grips with this site. Sidney
 
In principle it sounds fine to me subject to a few considerations.
1 the earth conductor connecting this second rod back the the main installations MET should be at least 6mm copper if my memory is correct and assuming it is not buried and is protected from mechanical damage etc etc.
2 the new earth rod should ideally be spaced from the existing rod by a horizontal distance equal to or greater than the sum of the lengths of both the existing and new rod.
The reason for this is that rods placed too close together will have overlapping spheres of influence, so under fault conditions will not achieve their best possible resist ace to earth.
But how on earth you will know the length of the existing rod I don't know! Even if the details of the original rod are recorded in the paperwork it will probably have been lost or eaten by the dog.
Apologies if this is teaching you to suck eggs, but it may be helpful to someone else reading the thread.




Sent from my iPad using Tapatalk
 

Reply to TT earthing system second rod in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
746
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
800

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top