Hi doing an eicr on a tt system, plastic board, bonding ok! It is a split 16th edition board with 80amp 100m/amp main switch which has the lighting, smokes and boiler on. On the other side is a 63amp 30m/amp rcd protecting sockets, cooker and shower. The Ra is 28 ohms.
anyway my interpretation of the regs is that for the circuits protected only by the main switch rcd that this would still merit a C3 for not be protected to 30m/amp, would you guys agree? Cables buried in walls less than 50mm and not protected via anything!
thanks
craig