TT or TNCS | Page 2 | on ElectriciansForums

Discuss TT or TNCS in the Australia area at ElectriciansForums.net

Joined
Feb 24, 2010
Messages
992
Reaction score
126
Location
South east
Greetings.
I am working at a friend of the families house helping to make the place safe and will be shortly arriving at the decision of what earthing system to use.
The house allready has an earth rod although the readings on it are rubbish.
The main bonding is giving an earth fault loop impedance of 18 ohms, much better than the rod I might add.
The suppliers have said TNCS is available but after reading much on the subject of earthing I'm a little undecided.
I have read about losing a neutral on the siupply side that is pretty much catastrophic if you have TNCS.
Also the neightbours electrical standards are pretty low from what I have heard and with TNCS I might be importing a whole lot of aggro from next door.
The thing that puts me off the earth rod is the high earth fault loop impedance. If the gentleman in question had a faulty RCD then if he had an earth fault no MCB's would trip, the earth fault current wouldn't be high enough with an earth fault loop resistance of 18 Ohms.
In doing my research I have realised some people have very strong views on this subject so I am asking which earth method would you prefer?
Thanks.
 
Last edited:
I had a PME connection done on a job recently for ÂŁ154 all in. Rods are adequate, but in my opinion PME is much better, especially as we are in 2010 not 1910.

Just an opinion and a preference.

Cheers..............Howard
 
with a TT syatem, you rely on the |RCDs to trip in case of a fault current to earth. The Mcbs cover L/N overcurrent/short circuit
Exactly, you have no second leyer of protection in case of an earth fault at all, only RCD's.
TNCS would give you this second layer of protection, RCD's and MCB's in the event of an earth fault.
 
agreed, you just got to weigh up the cost of TNCS, as sirkit says about 150-200quid. having said that, it's more reliable than TT.
 

Reply to TT or TNCS in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
204
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
805
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top