TT System High z's | Page 2 | on ElectriciansForums
Discuss TT System High z's in the UK Electrical Forum area at ElectriciansForums.net
B
bluecallum
Testing a property with a TT system all circuits are reading a high figure for earth loop impediance,any suggestions done a rcd test on circuits the other day and it was not tripping at 1x but today is but at 5x meter is reading 25v.
something inboard of the measured Ze point is causing this....
as you wouldn`t expect a value to suddenly shoot up by something in the order of 35 ohms...would you....
so i would suggest you start with the earth bar terminations....then move on from there....
Sorry mate.. still wrong.
Ze is 175
Zs is 145
You cannot calculate R1 + R2 by taking one from the other. Zs has parallel paths, which is why it is lower
OK...
so still the value of (R1 R2) is high....
and in fact given the parrallel paths would be worse if such parrallel paths were removed...
so the point is...the value of (R1 R2) is still miles too high.....yes?
- - - Updated - - -
oh rite....
sorry..
just re read it....
- - - Updated - - -
wondered where i was going then....
rite...
so for a start your circuit impedence (Zs) is 35 ohms...
what do you think?..
no. his Zs is lower than Ze due to parallel paths ( water and gas bonds). obviously, on TT systems he's got to rely on the RCD/s for fault protection Zs max. 1667 fo a 30mA RCD.
Reply to TT System High z's in the UK Electrical Forum area at ElectriciansForums.net
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...