Rewiring an older TT terraced property. There is currently 6mm earthing from the rod, and also as main bonding to gas and water. I (was!) confident that 6mm main bonding met the requirements of BS7671, but a fellow Part P installer insists that I need to upgrade the main bonding to 10mm, but that 6mm for the earth rod is satisfactory.
So, please could someone tell me the minimum CSA for the main bonding, and, if it is meant to be 10mm, how come the earth rod only needs 6mm? A reference or page number to the big book would also be helpful.
Many thanks