E
Engineer54
problem with your solution Dave is that most terraced streets built pre war dont have the available space to space road 10' apart. the advice i have always worked to is anything over 200 ohms should be deeemed not safe and regs state 1667 ohms
So working to that daft philosophy a value of 199 ohms is safe!! It actually says nothing of the sort it refers to an arbitrary figure relating to an earth electrodes stability.... Being happy with a 3 figure Ra value is a basic nonsense!! Oh, and what happens when that 30mA 1667 ohm RCD device you are totally relying on, fails to operate??
Nothing stopping you installing 2 or 3 5/8'' rods coupled together in the one location though is there?? Many of the older DNO supplies supplying TT installations have been PME'd. So the first course i'd be making, is contacting the local DNO to find out if this is the case in the area you will be working...