Not installed many earth rods then shanky? Lol

1/2" is closer to 13mm and 5/8 is more like 16mm
installed? no

i havent even seen one, i dont do any domestic and rarely do power from ccu either, usually from control panels.

i have done a couple boards but not many


but i do know enough about them that i could install one correctly (in earth put )and test it
 
Were they SPSN RCBOs or are they the standard SP RCBOs which are commonly available?

Was the person who told you that 2 rods is dangerous certified as insane or something? The whole country would be in serious trouble if this was the case!

Yes, it was on my last refresher course. The instructor did indeed state that he'd seen a few remote farm buildings where the installer had supplied another earth rod in order to make the disconnection times work. His point was that they should have been wired as two separate jobs, with individual earthing, not two rods connected on the same system. That way any fault would only go to ground at one location.

Can an overhead supplied TT system be upgraded to PME?
 
good point two inch holesaw is 51mm XD my bad 1"=25mm


1 ft. = 12".
3ft. = 1 yard,
22 yards = 1 chain
10 chains = 1 furlong
8 furlongs = 1 mile
1 rod = 5.5 yards
4 rods = 1 chain

there are 20 fluid ounces in a pint. 2 pints make 1 quart. 4 quarts make 1 gallon. that's a serious beer session.

here endeth the lesson.
 
1 ft. = 12".
3ft. = 1 yard,
22 yards = 1 chain
10 chains = 1 furlong
8 furlongs = 1 mile
1 rod = 5.5 yards
4 rods = 1 chain

there are 20 fluid ounces in a pint. 2 pints make 1 quart. 4 quarts make 1 gallon. that's a serious beer session.

here endeth the lesson.
id be on my backside after 3 quarts, i couldn't stomach a galon (i dont drink more than 2-3pints of water a day usually anyway
 
installed? no

i havent even seen one, i dont do any domestic and rarely do power from ccu either, usually from control panels.

i have done a couple boards but not many


but i do know enough about them that i could install one correctly (in earth put )and test it

Earth rods aren't limited to domestic work!

Have you done an earth rod test before then? It is something which seems to be missing from a lot of electricians knowledge, they can just about do the Bodgeit method with a loop tester, but many don't even know what a 3 wire fop test is!
 
Ra values can be improved ( lowered ) by the application of a pint or 2 of ale. the ale must be processed in the established manner before applying to the soil surrounding the rod. the first step is to drink the ale and then wait for the prescribed length of time, by which time nature has processed the ale, and you then apply it.
 
Earth rods aren't limited to domestic work!

Have you done an earth rod test before then? It is something which seems to be missing from a lot of electricians knowledge, they can just about do the Bodgeit method with a loop tester, but many don't even know what a 3 wire fop test is!
nope, most work is bms. power to our panels is usually done by others as well.

yes the earth rod test is using 3 leads connected

[ElectriciansForums.net] TT system main bonding CSA?


basically this in osg
 
Yes, it was on my last refresher course. The instructor did indeed state that he'd seen a few remote farm buildings where the installer had supplied another earth rod in order to make the disconnection times work. His point was that they should have been wired as two separate jobs, with individual earthing, not two rods connected on the same system. That way any fault would only go to ground at one location.

Can an overhead supplied TT system be upgraded to PME?

Nonsense! A single earth rod is far less effective than 2 in parallel! On a farm I would be looking to install a rod at each building and have them all linked together through the cpcs.
The more deep rods you have the better and more stable your Ra will be.

Installing them correctly will prevent potential gradients appearing on the ground.

Yes the DNO can convert their TT supplies to PME, if they have done this you can apply to have a PME connection made at the property.

Go and have a look at the overhead lines to see if they have done so in your area.
 
How would you no if they've converted it to a pme by looking at the overhead lines surely they just install a pme head

No they don't just install a PME head, they have to ensure that their network complies with the requirements for PME first.

They have to have N-E connections via earth electrodes at set distances along the entire length of the main, along with an electrode at the furthest point of the main (or furthest points if it branches)

In this area every pole with a N-E connection has a white label with PME in red letters fixed to the pole.

Also the use of ABC cable suggests that PME is likely to be available.
 

Reply to TT system main bonding CSA? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
608
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top