At the risk of asking a silly question could someone advise me on the following:

Client has a TT system with only half the circuits covered by an RCD, they want a light adding on a light circuit thats currently not covered by the rcd.

Now with half circuits not going to meet the disconnection times if I work on just the lighting circuit would I still have to cover all the circuits that haven't got an RCD with a new RCD or am I allowed to cover just the lighting circuit with an RCBO because that's the circuit i'l be working on?

Because of the results when testing I'm thinking i'm going to have to cover all the circuits but I'm just wanting to check the RCBO route incase the IR is low (old wiring) and nuisance tripping could occur (I know the clients won't be wanting to pay extra if I have to start going digging).

Thanks in advance
 
Yep found them thanks mate
6 064 16 LEGRAND 6a RCBO 30ma 10ka B TYPE
  • [ElectriciansForums.net] TT system, RCD or RCBO
  • [ElectriciansForums.net] TT system, RCD or RCBO
  • [ElectriciansForums.net] TT system, RCD or RCBO
  • [ElectriciansForums.net] TT system, RCD or RCBO
2
  • [ElectriciansForums.net] TT system, RCD or RCBO
ÂŁ25.95
 
A N-E fault on the lighting circuit you have altered will probably take out the RCD serving the rest of the installation. The only way to prevent that is a device which disconnects the N.
Ah yes I didn't think about the DP, if I remember theres a reg aswell that says TT systems need a DP..... they don't like making it too easy for the sparks do they haha!
 
My interpretation is that part of the installation is on an RCD and part isn't, it's possible that a N-E fault on the RCBO circuit could result in the other RCD operating for an unrelated fault because a parallel path would remain in place even if the RCBO tripped. A DP RCBO would prevent that. I do not think it is a requirement, but if possible I would fit a DP device if I was altering the circuit protection as part of the work carried out.
 
My interpretation is that part of the installation is on an RCD and part isn't, it's possible that a N-E fault on a single pole RCBO circuit could result in the other RCD operating for that fault because a parallel path would remain in place even if the RCBO tripped. A DP RCBO would prevent that. I do not think it is a requirement, but if possible I would fit a DP device if I was altering the circuit protection as part of the work carried out.

In my head it sounds like a tenby split load 16th ed board with first half Circuits direct from main switch and second half 30 mA rcd protected, thats the issue i usually find

It shouldnt affect the rcd downstream with an rcbo in place on the unprotected side but if there was another rcd (e.g. 100mA s type) between the origin and the new single pole rcbo, the N-E fault on the rcbo circuit would likely effect this device even when rcbo has tripped open and also cause the rcd to trip if sufficient load was applied through it

As such a double pole rcbo would be required to completely isolate said fault

Thats my understanding for what its worth

If an N-E fault would effect downstream rcd devices then i should think we would be in trouble combining RCDs onto PME supplies?
 
Last edited:

Reply to TT system, RCD or RCBO in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
594
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top