Hi all, a little stuck with a couple of things.
house on a TT system with a 16mm main earth and a 100A main cut-out.
the board has a 30mA 2 pole RCD main switch and all the circuits are 60898 protected.
One of the circuits supply's the garage with a 6mm 70 degree SWA. The garage, however is large and about to be converted into living accommodation with 250mm loft insulation and cellotex on the internal walls. There is a lounge, bathroom and kitchenette. The circuits are 32A shower circuit for a max 7.36 KW shower using 10mm cable because of the insulation. A 20a radial socket circuit for the lounge sockets wired in 4mm and the same for the kitchen sockets. Lighting will be low energy and will be 6A in 1mm.
There may also be an oven fitted so the worst case will be another 32A circuit.
The Cu will be 6 usable ways and have a 30mA RCD main switch.
I intend to replace the supply cable with a 90 degree thermosetting SWA 3c 10mm, protected by a 63 A C/B
If there is a fault in the garage there will be no discrimination and the whole lot will go out and the reverse is also true
I am going to strongly recomend they change the main CU for a 17th edition type with two 61008 30mA for the house circuits and as it's a TT system a 100mA S type main switch. How should I protect the supply cable? Do I run it from a separate non RCD protected way in the CU and rely on the 100mA S type of the main switch?
house on a TT system with a 16mm main earth and a 100A main cut-out.
the board has a 30mA 2 pole RCD main switch and all the circuits are 60898 protected.
One of the circuits supply's the garage with a 6mm 70 degree SWA. The garage, however is large and about to be converted into living accommodation with 250mm loft insulation and cellotex on the internal walls. There is a lounge, bathroom and kitchenette. The circuits are 32A shower circuit for a max 7.36 KW shower using 10mm cable because of the insulation. A 20a radial socket circuit for the lounge sockets wired in 4mm and the same for the kitchen sockets. Lighting will be low energy and will be 6A in 1mm.
There may also be an oven fitted so the worst case will be another 32A circuit.
The Cu will be 6 usable ways and have a 30mA RCD main switch.
I intend to replace the supply cable with a 90 degree thermosetting SWA 3c 10mm, protected by a 63 A C/B
If there is a fault in the garage there will be no discrimination and the whole lot will go out and the reverse is also true
I am going to strongly recomend they change the main CU for a 17th edition type with two 61008 30mA for the house circuits and as it's a TT system a 100mA S type main switch. How should I protect the supply cable? Do I run it from a separate non RCD protected way in the CU and rely on the 100mA S type of the main switch?