mannex

-
Joined
Mar 31, 2013
Messages
12
Reaction score
1
Location
United Kingdom
I am working on a TT system and the electrics are tripping all the time, I have narrowed it down to the downstairs light circuit. Everytime when this light circuit is connected at the board and if I try to turn the oven (on the cooker circuit) or boil a kettle. ( ring main) it trips the electrics, but when the lightning circuit is disconnected everything works fine. I have done the insulation. Test and its ok am now running out of idea. Because it seems the lighting circuit is interfering with the cooker circuit and ring downstairs main. But how its happening........... I am hitting a brick wall.

Help please

I had to reposition a light switch on this light circuit and I have since double checked my wiring. The rcd is tripping not the mcb
 
Last edited:
The reason the RCD is tripping is you've probably got a N-E fault on the lighting circuit.

When you have a high current appliance on (oven/kettle) then the resistance of the fault is small enough to divert a small amount of current through the N-E fault!
 
Mannex your profile says your still in training, have you got a mentor or are you doing this job alone, also you say you're working on the lights is this to fix the fault or has the fault occurred whilst working on the circuit.
Can you give us as much info as possible.
 

Reply to TT system tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
349
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top