Everything seems to be covered regarding the earthing on here now and regardless of what earth system is at the origin I like wirepuller would use that earth to protect the SWA by connecting the armour at that DB and then leave it open at the new 3 phase DB.
Again as wire says I you would batch the connections points to the maximum allowed which is 4 and rod each point of connection, so 1 rod would do your 4 sockets. Though of course each Ra would be taken at each point until IMO you got below 100ohms, I know it is 200 in the BS 7671-2008 but I would work to BS 7430 in this case.
The only thing I would bring to the table is perhaps running the points in a ring main. As 300 mts being your furthest point by doing in a ring main you could utilise a smaller SWA
Again as wire says I you would batch the connections points to the maximum allowed which is 4 and rod each point of connection, so 1 rod would do your 4 sockets. Though of course each Ra would be taken at each point until IMO you got below 100ohms, I know it is 200 in the BS 7671-2008 but I would work to BS 7430 in this case.
The only thing I would bring to the table is perhaps running the points in a ring main. As 300 mts being your furthest point by doing in a ring main you could utilise a smaller SWA