Trying to be clever over a typo?? lol!! You stick to your 200 ohms Ra, your obviously a one, or single rod man.... good luck to you!!!
For your information, i am on a TT system here!! have brought Ra values down to below 20 ohms Iby the use of just 2 further rods to the system, on quite a few of my friends properties here. Mine is 3 ohms in winter and 5 to 8 ohms in the summer, but then i made the provision of having the steelwork of my house foundation to be available for connecting to my TT system, along with other structures steelwork on my property!! There is a hell of a lot more to TT systems than bunging a rod in the ground!!
Once you have a decent Ra value, you then have to maintain that value, ...Now how many electricians in the UK that quite happily create a so-called TT system, can instruct the home owner or client how to maintain those systems, ...not many at all, i fear!!!
Your right, i don't have the current BS7671 as yet, Does that mean i don't know what i'm talking about?? On this subject, i think i'll rely on my training, my working experience, and the knowledge i've gained over the 35 years i've been in this industry, ...after all, my employers are more than happy too!!!
If you actually had a copy of Bs 7671 you would realize that a value in the region of 20 ohms will result in a Zs far too high to operate an overcurrent device,even values of 5-8 ohms will be too high for most. Which means you are STILL reliant on the RCD to provide fault protection....which kind of negates your argument.