8 circuits
Wylex
Could i put a 100a 100ma type s in an enclosure before the board then leave the rest?
if u used dual rcd consumer unit with 30ma rcd protection to all circuits then 100ma s rcd is pointless 30ma rcds and rcbos will give you earth fault and additional protection your 100ma s rcd is protecting nothing as 30ma would always trip first
Really!!!! So what is protecting any of these circuits when either one of the RCD's fail in a dual CU, or if any of the RCBO's fail in an all RCBO CU??
We don't know what the Ra value of this installation is, but it's a pretty sure bet, that the usual single short thin twig has been employed as the earth electrode. So were probably talking of an unstable made electrode with an Ra value hovering around this magic 200 ohms. So let's hope that none of these RCD'S/RCBO's fail!!! The 100mA S type up front RCD will give a TT installation additional protection it needs....