Really!!!! So what is protecting any of these circuits when either one of the RCD's fail in a dual CU, or if any of the RCBO's fail in an all RCBO CU??
We don't know what the Ra value of this installation is, but it's a pretty sure bet, that the usual single short thin twig has been employed as the earth electrode. So were probably talking of an unstable made electrode with an Ra value hovering around this magic 200 ohms. So let's hope that none of these RCD'S/RCBO's fail!!! The 100mA S type up front RCD will give a TT installation additional protection it needs....
Fair play.
How many circuits?
What make is the board?
Change the 30mA for 100A 100mA s type & plonk in 30mA rcbo's for circuits................or change the board for a dual rcd board.
Customer has a tt system with a 30ma rcd as main switch on cu. would you upgrade this board and put type s in or..??
why an S type?.....Personnaly i would upgrade but looking for advice as not long tome served and i knew someone could help me on this. And if ur not sure better to ask some one with more experience
Do the Regs say you have to fit a 100mA S type RCD? I know the onsite guide shows one, or used to show one, but do the Regs stipulate it?
look....
if you have a garage.....and wish to give the garage 30mA RCD (for fault) at the garage end......then you would typically use an armoured to feed the garage of ov a 100 mA S type top end .......so whats the meanin of feedin the house c/u with a 100 mA S type as an `upgrade`.....lolffs..
Only on a TT system Glenn. It's 100mA and time delayed because of discrimination, and it'll be looking at the total/combined leakage of both RCD's in a dual board or all RCBO's of an all RCBO board. To my mind all domestic TT installations should be full RCBO boards!!
The S type, basically backs up the standard RCD devices that fail to operate... Given that most UK TT systems have been installed around that numbty 200 ohm Ra, it's more than prudent NOT to totally rely on two single 30mA RCD devices for the installation, or circuit (RCBO's) earth fault protection.
I got mine! Off eBay, sealed, 32 sobs. Bargain! (Oh, and OSG, GN3, d'led Part P and other pertinent bits as per building regs guides, but I'm a smug bugger!! :biggrin5Just goes to show they teach sod all during these nifity 5 week courses LOL
Sounds as though every new comer to the trade either can't read or because they undercut everyone to get the work, can't afford a copy of the regs:rant: