And you chaps would be happy to leave a TT installation with a high Ze albeit within 1667?
Not sure i would.
Not sure i would.
The maximum permissable resistance on an earth electrode with 30ma rcd protection is 1667ohms.....the 200 ohms value quoted is only advice that anything over that value may be unstable...... anything under 1667 ohms will comply with the regulations.I'd only be worried if I had a very high resistance when the ground was already very wet and likely to dry out further.
The 1667 figure quoted in the regs book is for maximum Zs not earth rod resistance.
It is recommended that the earth rod be <200 ohms for conformance with 542.2.2