Discuss TT Systems in the UK Electrical Forum area at ElectriciansForums.net

AdieB

-
Joined
Apr 1, 2012
Messages
76
Reaction score
6
Location
Dorset
Hi quick question I have to change a consumer unit out. It is a TT supply system. All breakers will be 61009. I have spoken to my part P tech department and they say that I still need a 100A 100mA S type main switch up front. Another guy says NO as the breakers are all 30mA controls. The first guy said it was required incase there was a neutral fault. But as the neutral also connects into the 61009 will that not provide protection?

AdieB
 
There isn't a requirement as far as know to install an S-type upfront although wouldn't be a bad thing either if you did...the rcbos would have to be double pole or single pole switched neutral.
 
Last edited:
There isn't a requirement as far as know to install an S-type upfront although wouldn't be a bad thing either if you did...the rcbos would have to be double pole or single pole switched neutral.

I was going to use a Lewdon board with RCBO - */30/SP which is single pole but if you look at the diagram it shows that the RCBO coil is looking for out of balance between phase and neutral which would result in a trip. Would this not provide adequate protection?
AdieB
 
I was going to use a Lewdon board with RCBO - */30/SP which is single pole but if you look at the diagram it shows that the RCBO coil is looking for out of balance between phase and neutral which would result in a trip. Would this not provide adequate protection?
AdieB

You shouldn't need the diagram to know that it compares line and neutral!
But no that does not provide protection against neutral faults as it will not clear a neutral fault, only detect it.

Think about what will happen if a neutral to earth fault occurs, the rcbo will detect the flow of diverted current from neutral to earth via the fault and then disconnect the line leaving the diverted neutral current flowing through the fault making it nice and hot ready to start a fire
 
And for that reason a dual RCD board would be better, but surely Dave when the line is disconnected by the individual RCBO, fault current from neutral to earth in that circuit will also cease ?
 
No, because N-E fault current could be from any or all circuits not just the faulty one. The neutrals are all commoned in the busbar and current can just as easily flow out to the fault from the DB as back from the load on the faulty circuit. Hence the need for DP switching to disconnect 'both ends' of the faulty neutral conductor.
 
Last edited:
And for that reason a dual RCD board would be better, but surely Dave when the line is disconnected by the individual RCBO, fault current from neutral to earth in that circuit will also cease ?

The neutral current from that circuit will cease yes, but it will continue to be diverted from the rest of the installation, hence the overheating of the N and E conductors (if it was just the one circuit's neutral current then this wouldn't be an issue)
 
Is there a regulation that says all TT systems with 61009s fitted on all circuits has to have a S type 100A 100mA DP RCD up front. I can not find one. Out of two Napit Tech guys say there is not a requirement. I have also just received a copy of a previous EICR of a job that requires retesting where again it is a TT system with a 100Amp isolator controlling two DP 80A 30mA ( split board) which then controls 60898 mcb's so is this ok as the RCD's are DP? Or should the main isolator be 100mA DP S type as the 30mA will trip before the 100mA
 
Hi AdieB
During my recent NICIEC assessment I was advised to fit a 100mA S type RCD up front on TT systems, because the CUs are now steel and have the additional risk of an internal SC between the flexible conductors that supply the RCDs and earth. It actually states this in the yellow On Site Guide on page 34 below the twin RCD diagram. Two other solutions for TT systems are shown on page 33 - the second showing RCBOs on to a solid busbar not requiring the S type RCD up front.

Cheers
Pete
 
Thanks for the reply I will check my yellow book which is in van. The two boards I am speaking about are both plastic / polycarbon type did your guy say anything about this type of board?
 
Just reviewed book and if I am reading correctly if you install an AMD 3 metal board on a TT system then you have to install a 100mA 100A rcd external to consumer unit not as a Main switch.
 
Just reviewed book and if I am reading correctly if you install an AMD 3 metal board on a TT system then you have to install a 100mA 100A rcd external to consumer unit not as a Main switch.
I would phone your CPS technical line and see if they class an RCD as similar switch gear and if they regard it as such then it would have to be housed in a non combustible enclosure so IMO would be pointless installing it externally and may as well swap the main switch for a 100mA s type RCD. I've seen it argued a few times that an RCD may not be classed as similar switch gear as offers no over current protection....IMO I think this is wishful thinking and would have to be housed/enveloped in a non combustible enclosure. I think the general consensus is to take the tails through a purposely made nylon tail gland, adequately support the tails from the board to the meter to minimise movement and replace the main switch for a 100mA S-type to provide earth fault protection to the flexible links that feed the RCD's on a dual RCD board.
 
Last edited:
There is no requirement in BS7671 to provide RCD protection specifically for TT installations.
It may be necessary to use an RCD to provide earth fault protection due to high earth fault loop impedance.
Traditionally a 100mA 'S' type RCD was installed up front.
Where the 100mA 'S' type RCD was installed in a metal CU, an insulating gland would be used where the tails entered the CU.
The 100mA 'S' type RCD would allow discrimination for any downstream 30mA RCDs.

As far as I am aware, no RCDs will detect a loss of supply neutral.
However RCDs/RCBOs with a functional earth will operate in the event of a loss of supply neutral.

Where all circuits are provided with individual 30mA RCD protection, there is no reason to install an up front 100mA 'S' type RCD.
Where a metal split type CU is used, then an upfront 100mA 'S' type RCD will provide protection to the internal wiring of the CU.

Double insulation provides earth fault protection to the tails upstream from any RCD.
 
Just reviewed book and if I am reading correctly if you install an AMD 3 metal board on a TT system then you have to install a 100mA 100A rcd external to consumer unit not as a Main switch.

Answering your first question - If they're plastic boards a Main Switch and two 30mA RCDs is fine in a TT situation. I assume these are for a non- domestic application?!

On this question, for a metal board in a TT situation, the S type RCD can replace the Main Switch see Figure 3.6.3(ii) on page 33 of the yellow On Site Guide.

Pete
 

Reply to TT Systems in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
778
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top