Prior to A3, the recommendation was an insulated CU on a TT supply, because there was a risk, however small of a metal CU becoming live, because of the conditions previously mentioned.
Now with A3, a non-combustible CU must be used for all supplies on a domestic property, ferrous metal being the suggested material. Therefore the 'grown-ups' have had to come up with a recommendation for using a metal CU with a TT supply. The yellow OSG has made those recommendations, and using workmanship procedures & suitable products.
Hence 100ma S Type RCD as main switch, to prevent single insulated internal cables (manufactures) between said S type & dual RCD's, making live accidental contact with metal enclosure, or the use of RCBO's (no S Type RCD) with the chance of internal busbars (connecting the live side of RCBO) 'minimal'.
The use of 6181y cable as tails, with suitable gland, negate the use of stand alone S Type RCD, outside of CU.