I have just come across a domestic installation that has two consumer units I was asked to wire extra sockets and do a board change as well. I found that the sockets of one board circuit are interconnected to a circuit from the other board, thus back feeding each other. This means that unless you isolate both boards or pull both relevant fuses then the whole installation remains live. I have wired my additional sockets to my own board , and explained to the client what the problem is. There is no way to find where these two circuits are interconnected without ripping up boards or going in loft and emptying it. And it's a possibility that it's been done more than once. Apart fron putting a warning notice for two sources of supply what am I meant to do. Mention of tearing the house apart was not well accepted.