Two single phases through one isolator? | on ElectriciansForums

Discuss Two single phases through one isolator? in the Commercial Electrical Advice area at ElectriciansForums.net

S

schooleydoo

Morning guys,

I'm new to this so bear with me!

I have two 16a single phase machines that I want to supply with a single cable. I want to use one neutral and earth for two separate circuits. Is this possible? I seem to remember when N is a load carrying conductor, combining two loads could burn it out?

Also, can I use a three phase isolator switch (like this) and just leave L3 empty?

Like this:

[ElectriciansForums.net] Two single phases through one isolator?
 
Last edited by a moderator:
bad design there, mate. as it's drawn, your N cable has to carry the load of both machines.
 
Yeah thats what I was wondering too, with my load carrying conductor comment. Ah well, thank you for clarifying :)

Assuming no problems if I took two Neutral lines back to the consumer unit? Any ideas on the switch?
 
you could feed to the isolator in 6mm, then split to the 2 ocpd's in 2.5mm, 1 for each machine. however, i would fit separate isolaters, each 1 fed from DB, with the ocpd's in the DB, not after the isolator. the feed has to be protected at the DB with MCB/RCBO, so why fit additional ocpd's?
 
Last edited:
I think I may be overcomplicating things!

We are installing machines at a industrial site. The customer wants to be able to switch both machines on from a single point, at the machine itself. So I want to put both machines circuits through one isolator switch and mount on the side of the machine.

I wasn't sure about the customers protection on the DB, so thought it best to protect our machines ourselves.

The customers supply will be three phase. So I thought I could use L1 for machine A, L2 for machine B and terminate L3 at my isolator switch and go no further with it. I would then run two Neutral lines back to the DB, one for each machine. Would this work?

The only problem I can foresee is A - running two neutral cables through one isolator switch and B - their 3 phase supply will only have one Neutral. If the cable dia was correct, could I use one N for both machines load?
 
Last edited by a moderator:
each m/c is 16A, so from a 40A MCB, 6mm to isolator. L1 for m/c 1 L, L2 for m/c 2 L, L3 for N. then cable each m/c in 2.5mm, fitting appropriate size OCPD (16A)for each.
 
don't forget, the isolator needs to be rated for both loads added. say a 40A.
 
Using two phases at 16A, one per machine you will have 16A in the neutral. So loading of the neutral shouldn’t be a problem. But I will say I don’t like the set up.
 
Havent really had time to think about circuit arrangement but can anyone see a use for contactors in this scenario? Maybe arrange two seperate circuits from DB through contactors?

Not really my area of expertise so I can't say for sure.
 
Got it, massive thanks everyone :)

Also just found out machine 1 is actually 13a, machine 2, 12a. So downgraded to 32a protection.
When you say L3 for N, this is from my switch onwards, correct? I can't use the L3 line all the way back to the DB can I?! This will not be a balanced load.

Switch - Buy Non-Fused Switch Disconnectors 3P open type switch disconnector,32A Ie Telemecanique VBD1 online from RS for next day delivery.

MCBs - Buy MCBs 16A MCB 2 Pole Type B ABB S 202-B 16 online from RS for next day delivery.



[ElectriciansForums.net] Two single phases through one isolator?


The earth will come straight into our PE terminal inside the cabinet from the supply line, it will not go through the isolator. Is this OK? Technically in the event of an earth fault, you probably need to be able to isolate the machine? But if there is an RCD on the DB, it would protect it anyway...
 
Last edited by a moderator:
Why do the machines have to be on different phases why not put them both on one phase protected at 32a and use a single phase isolater and double up on the outgoing side of the live and neutral side this also eliminates the chance of having 400v between the 2 machines if they are close together and the person using them safer in the event of a fault

Sent from my GT-I9100 using Tapatalk
 
Forgot to mention make sure you add your own protection for each switch after the isolator 16a should be fine as they are machines and may have motors on them

Sent from my GT-I9100 using Tapatalk
 
4 pole Isolator
L1, L2 on 2 poles
L3 secured in a terminal block within the box.

Loop the neutral across the other 2 poles on the incoming side.

The isolator only needs to be rated at the highest of the 2 loads, but I'd use a 20amp as a minimum.

Then whatever protection you want for each machine after the isolator

How far away from the master isolator is the 2nd machine, you may still need a local isolator for that, or is it built in?

The earth will come straight into our PE terminal inside the cabinet from the supply line, it will not go through the isolator. Is this OK? Technically in the event of an earth fault, you probably need to be able to isolate the machine? But if there is an RCD on the DB, it would protect it anyway...

You can't run the earth separate, it needs to be with the phases, if it travels a separate route it may get accidentally disconnected.
I can't quote a reg for this but there must be one.
 
Last edited:
Electraz, that would be ideal but the customer doesn't want to change their existing power drop to the install area or DB.

Snowhead... 4 pole as in 3P+N? As far is I can tell, there is no earth on these? So I assumed it just bypassed the isolator but like you, would be surprised if it wasn't supposed to be switched.

So with your method I would be using L1 and L2. L3 would not run through the switch but safely terminate inside the cabinet and remain unused. N would split after the switch as per my drawing above. I don't understand what you mean by looping N between two poles on the incoming side though? A jumper cable Between L3 and N? Why? Just to make splitting N tidier? Out of L3 and N on the switch output.

The two machines are actually inside one enclosure, about 500mm apart. This is machine A's enclosure. You can see the main isolator on the side, running up to the MCB and onwards. Machine A is a UV dryer. Machine B is a plasma generator.

[ElectriciansForums.net] Two single phases through one isolator?
 
Last edited by a moderator:

Reply to Two single phases through one isolator? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
674
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top