Underground SWA Cable | on ElectriciansForums

Discuss Underground SWA Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

skyline2500cc

A new supply has been installed by SSE and its a single phase TN-C-S in other words neutral and Earth combined at the cutout or point of supply.
Meter tails have been installed to a distribution board which feeds one circuit. From that distribution board we need to run a SWA conductor from an MCB, 600 meters underground to an outbuilding which will have another distribution board to feed additional circuits.
We have looked into the cost of a 3 core SWA copper cable and its between 4-5K. I was wondering as the earth and neutral are combined do the regulations permit you from running a 2 core i.e Live and Neutral and using the SWA or (CPC)
as the earth.
Look forward to any advice
:icon12:
Skyline2500cc
 
what size conductors in the SWA? generally armour is good for cpc up to 95mm or thereabouts.
 
Hi Telectric
Thanks for your response we are looking at 70mm2 CSA. The question I would like to know is there any technical, or regulatory reason why the SWA could not be used, saving us the expense of the third copper conductor.
Regards
Skyline2500cc
 
600 metres is a long run for an LV cable. I'd imagine that volt drop will be your biggest challenge.

With regard to earthing, you can always make the remote end a TT installation so you're not reliany on the TNCS earth.
 
Hi Telectric
Thanks for your response we are looking at 70mm2 CSA. The question I would like to know is there any technical, or regulatory reason why the SWA could not be used, saving us the expense of the third copper conductor.
Regards
Skyline2500cc

It is permitted, but you'll need to do all the necessary calculations to ensure it complies with BS7671. If you have any extraneous parts in the outbuilding you'll need to consider bonding them. You may be better to use TT, but the volt drop will still be a big factor to consider.
 
70mm 2 core SWA has a CSA of armouring of 84mm2 ,with 70mm 2core the required CSA of the armouring would be 79mm2 so using 70mm two core SWA will be fine.
 
The armoring will only be suitable for the circuits CPC, not if this building needs any extraneous metalwork bonding.

Just be aware of your Zs for a circuit this long, in the past I have used enhanced conductive SWA, one armor strand in 5 was copper coated to get around it.
 
Our advice is baseless until the OP divulges the calculated load of this shed and also whether it has structural steel and/or other services in metal.... as it stands the advice given has no bearing until we know these points.

Also a discussion with the DNO will be needed to enquire if additional earthing would be required due to the Network set-up if this other building requires any sort of bonding.

So lastly what is the CSA of the SSE supplied N to the service cutout?

At these distances 70mm might give you enough power to boil a kettle and be within acceptable VD of 3% assuming lighting load.
 
Last edited by a moderator:
Just be aware of your Zs for a circuit this long, in the past I have used enhanced conductive SWA, one armor strand in 5 was copper coated to get around it.

I didn’t think they still made that.

I was looking for some before I retired to extend a PILC. I gave up in the end and took a separate CPC out of the end of the through joint. It looked like a bizarre breach joint.
 
Depends how deep your pockets are, I had 300m at an eye watering amount the last time I used it.

Christ must be 10years ago now, doesn't time fly.
 

Reply to Underground SWA Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
346
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
885
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top