martinsayer81

hi guys

hoping you could give me your thoughts,

i am pricing for a consumer unit change, its an old fuseboard with re-wireables.
it has 16mm meter tails, but it has a fairly new looking 100A main fuse.

its a small-ish house..... 2 ring mains, 2 lighting radials, a couple of sockets in the garage, and an immersion heater radial,

i was wondering whether or not i could just down-grade the main fuse to a 60A and keep the existing 16mm tails( no damage, or signs of overheating or burning)
or whether i have to leave the fuse at 100A and fit 25mm tails?

there's no electric shower or oven,

i would appreciate your advice

many thanks
 
murdoch needs more than a troll badge ,guys obviously got issues and comes on here looking to see what post he can annoyingly comment on ,
SADDO
 
yeah i agree its a forum ,free speech,etc etc sparks helping other sparks out with varieties of knowledge but some guys are just arrogant ,
the type of guys that sit there self at lunch , that no one likes
 
murdoch needs more than a troll badge ,guys obviously got issues and comes on here looking to see what post he can annoyingly comment on ,
SADDO


For someone with only 52 post and no thanks I think you need to adapt your approach if you're to remain on this forum. Step over the line and the mods will throw you off.

- - - Updated - - -

murdoch needs a troll badge, you troublemaker you lol.

Troll badge - cool!
 
For someone with only 52 post and no thanks I think you need to adapt your approach if you're to remain on this forum. Step over the line and the mods will throw you off.

- - - Updated - - -



Troll badge - cool!
can i taunt him for a bit murdoch......i can 100% guarentee that he wont be back after a taste of my argumentative skills....lol...
 
all my customers appreciate my good quality work,knowledge and professionalism so my advice is golden to them its not much of a hassle to have this done actually can benifit in future , they are there for a reason thats why every new build will have L in and out of switch and nuetral in & out

Which planet are you on?
 
You only NEED 25mm tails is if there is a 100A cut out fuse. Otherwise 16mm will be fine!! It may be prudent to realise that a 100A cut out fuse can only be provided when the Ze/Zs available is adequate to provide clearance times....

I have yet to see a typical standard to large domestic installation come anywhere near drawing a 100A or anything close to it!! Far too many here take more notice of a guidance drawing in the OSG, than using their training and commonsense!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
upgrade meter tails, or downgrade main incoming fuse??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
63
Unsolved
--

Advert

Thread statistics

Created
martinsayer81,
Last reply from
Engineer54,
Replies
63
Views
14,678

Advert

Back
Top