Hi folks, about to do a domestic PIR and observed during survey that the main earth conductor is flat braided copper. Didn't measure but from photo it looks either 6 or 10mm2 CSA. Assuming that Captain Adiabatic tells me it's inadequate, when I call on supplier to upgrade, will they most likely replace with larger braid or put on a new sheath clamp with appropriate round cable? Many thanks, SW
 
Here you go...

IMG_0626.JPG
 
Did you get the measurements of it?


Nominal area (mm²)Width (approx. mm)Thickness (approx. mm)Wire diameter
[TD="class: table_content_left"]6[/TD]
[TD="class: table_content"]12.0[/TD]
[TD="class: table_content"]1.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]10[/TD]
[TD="class: table_content"]15.0[/TD]
[TD="class: table_content"]1.5[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]16[/TD]
[TD="class: table_content"]19.0[/TD]
[TD="class: table_content"]2.5[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]25[/TD]
[TD="class: table_content"]25.0[/TD]
[TD="class: table_content"]3.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]35[/TD]
[TD="class: table_content"]25.0[/TD]
[TD="class: table_content"]4.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]50[/TD]
[TD="class: table_content"]30.0[/TD]
[TD="class: table_content"]5.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]70[/TD]
[TD="class: table_content"]32.0[/TD]
[TD="class: table_content"]6.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]95[/TD]
[TD="class: table_content"]37.0[/TD]
[TD="class: table_content"]6.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]120[/TD]
[TD="class: table_content"]45.0[/TD]
[TD="class: table_content"]6.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]150[/TD]
[TD="class: table_content"]50.0[/TD]
[TD="class: table_content"]8.0[/TD]
[TD="class: table_content"]0.20[/TD]

[TD="class: table_content_left"]200[/TD]
[TD="class: table_content"]50.0[/TD]
[TD="class: table_content"]10.0[/TD]
[TD="class: table_content"]0.20[/TD]
 
Last edited by a moderator:
It's the DNO property mate and all you can really do is call them, but I know that if you have a good Ze value for it they will do nothing.

If I got a good Ze value, then I would basically leave it alone, You could note it, but it's not part of our installation so as long everything the customer side is ok then your good.

It may even be an old DIY TN-S done by a bygone sparks
 
i=p/u, no, it's not just a water pipe. Why would an electrician post a picture of a supply cable with an earth strap around it and ask what the DNOs approach would be if it was a water pipe? Let me quote you something:

"aint easy isit, dealing with cable pullers like myself. ive no expierience with testing so just done R1+R2 with multimeter"

A 16mm2 earthing conductor is not strictly required if the adiabatic equation allows it. But, I had not appreciated, per malcolm's comment, that this may be a DIY TN-S, in which case, the DNO would state they are not supplying an earth. What would happen then if there was an incident (this property has no RCD). If I'd done a job and walked away, yes, I probably be liable.

One needs to be very careful giving technical advice or commentary on a forum like this. Because a DIYer, an apprentice or someone with little experience might (foolishly) take the advice and then go and kill themselves or someone else.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Upgrade of fat braid main earth conductor
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
SW1970,
Last reply from
La Poste,
Replies
30
Views
4,317

Advert

TrueNAS JBOD Storage Server

Back
Top